Discuss how to upgrade the earthing conductor? in the Industrial Electricians' Talk area at ElectriciansForums.net

No no I understand. And I also understand why British Gas weren't happy installing with that behind it and personally I'm happy to upgrade it, also because DNO are going to change it to a PME.
 
i may be inaccurate here, but theoretically the protective device, usually a 1361, will blow long before the fault current gets anywhere near it's rated breaking capacity of 16kA. it's a very rare occurence for a fault current to develop upstream of the circuit protective devices, although not unknown.

BS 1361s have a breaking capacity of 16.5 or 33kA depending on type. Think you might be thinking of the fact that if you have a CU to BS 5486 or BSEN 60439 then the enclosure is rated to withstand high PFCs and you can then record max short circuit capacity as 16kA if you have a BS1361 or BS88 (less than 100A)
I was just making the point that if someone is thinking "oh i'll upgrade the earthing" without full consideration, especially if they have older style CBs or BS3036s, which certainly won't be in such a CU, then they could be opening a can of worms as their short circuit capacity could well be 1, 2, or 3kA.

Must admit i only glanced thru the thread so don't know the full details as to whether a CU upgrade was being considered as well.
 

Reply to how to upgrade the earthing conductor? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K
I've come to a decision, I just cant do work anymore that involves mad stuff, for example today - 2 bed flat that's had fire damage, someone has...
Replies
4
Views
828
Just a bit of a muse at the moment, work won't happen for a while, though I do already have the ducting. We have (what's left of - it was rotten...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock