I have a quick question which I wondered if anybody would be kind enough to answer for me.

I'm looking to buy an electric car and would need to get a car charger installed on the outside of my garage wall so I posted on an electrical car forum and have been told our electrical setup may not be suitable.

I live in a 5 year old detached house which has a separate garage at the end of the garden (approx 10 meters away). The garage has electric and has been fed via a cable which runs under the lawn and into the house which goes through the brickwork and into the back of the dining room wall socket.

The garage is on the same fuse as the rear of the house sockets so the only way to isolate the isolate power to the garage would be to knock out half of the house sockets.

I've been told on another forum that this setup is not right, the forum :

"This diagram shows what is acceptable as a spur off a ring main. As you will see anything bar one socket on a spur needs to be protected with a FCU.
https://www.diynot.com/diy/media/ring-main.11895/full?d=1243854953

You may have some restitution under the NHBC scheme."

Can anyone shed any light on this for me please? Is our setup against regs?
 
It may not be acceptable depending on what else is in the garage and the type of car charging load. If a single cable is run from a ring final circuit that is classed a s a spur, and a spur may only supply one single or twin outlet. If the spur is run through a 13a fused connection unit then unlimited sockets may be connected to it but the load will be limited to 13a. Car charger points may be 13a, 16a or 32a. It would only be possible to utilise a spur off a ring for a 13a point. There is also a special location section in the regulations for car charger points, and your final installation will need to comply with those requirements, with restrictions on type of earthing etc. Your garage installation may not meet those requirements. Get an installer to check it out for you.
 
Last edited by a moderator:
If it were a much older house, you might expect something like that (regardless of whether it's right or not) - on a 5-year-old property? I'd be making inquiries as to how on earth the developers signed that off.
 
If it were a much older house, you might expect something like that (regardless of whether it's right or not) - on a 5-year-old property? I'd be making inquiries as to how on earth the developers signed that off.
Unfortunately I have seen more than a few new builds where the garage power is a radial off the kitchen RFC. Ugh !
 
From my experience with house builders , a lot of them done away with detached garages being wired as standard (especially the smaller houses) and made it a extra. This had the knock on effect of unless contracts were exchanged it would not be wired and unfortunately this meant that in some cases the feed for the detached garage would be taken from the back of a socket.
 
As I said you need to do some reading.
It’s all made very clear in the IET code of practice for electric vehicle charging equipment installation.
 
Agree with that.
If source is PME then it needs to be TT if it's mounted outside a building. This is also dependent on your own risk assessment providing evidence there are no simultaneously accessible extraneous parts belonging to the PME system.
There is currently a "get-out" which allows use of PME "if not reasonably practicable". I suspect that is being used more than sensible by many EV charger installers. This also relies on a credible risk assessment (your neck being on the line in the court) to say that's all OK for whatever reasons you choose. The latter get-out will disappear completely in 18th as I believe.
And don't forget that the TT earth you provide needs to be LOW. Chargers (certainly 32A ones) will monitor EFLI and not allow charge if it's too high. Notionally 200 ohms, but don't believe it. I have it on good authority from a Renault tech that their chargers might need as low as 70 Ohms to operate reliably. - That is likely to need more than a 4' twig in the soil.
And don't forget type A RCD and probably a D type breaker.
 
Agree with that.
If source is PME then it needs to be TT if it's mounted outside a building. This is also dependent on your own risk assessment providing evidence there are no simultaneously accessible extraneous parts belonging to the PME system.
There is currently a "get-out" which allows use of PME "if not reasonably practicable". I suspect that is being used more than sensible by many EV charger installers. This also relies on a credible risk assessment (your neck being on the line in the court) to say that's all OK for whatever reasons you choose. The latter get-out will disappear completely in 18th as I believe.
And don't forget that the TT earth you provide needs to be LOW. Chargers (certainly 32A ones) will monitor EFLI and not allow charge if it's too high. Notionally 200 ohms, but don't believe it. I have it on good authority from a Renault tech that their chargers might need as low as 70 Ohms to operate reliably. - That is likely to need more than a 4' twig in the soil.
And don't forget type A RCD and probably a D type breaker.

I think you need to do some reading too :)
 
page 26
its also in your bs7671 page 279
Why make it all TT when you can just connect the rod to the MET like i think they are asking in the 18th
 
It says that if you can't meet the requirements you can still use TN system if its a dwelling. The code of practice goes on to say that there are way to help reduce the touch voltage as getting the required low Ra is unlikely. I'm not saying it does not happen but how many open circuit PEN installations have you been to?
 
It does, and I have needed to do that when moving a charger. (Lots of very sandy dry soil near here). I believe that it won't allow that any more in 18th edition.
 
It says that if you can't meet the requirements you can still use TN system if its a dwelling. The code of practice goes on to say that there are way to help reduce the touch voltage as getting the required low Ra is unlikely. I'm not saying it does not happen but how many open circuit PEN installations have you been to?

There have been two open circuit PEN conductors on our estate alone. Both were faults in the joint boxes (installed circa 1974) underneath the pavement feeding the houses. In fact, one was at my house and resulted in my wife receiving a shock from the metal-clad lightswitch in the garage. Never assume it can't happen - there are a hell of a lot of those joint boxes out there.

Oh and they came out pretty quickly to the fault! They fitted a temporary bit of concentric from my neighbours cut-out across the drive to mine. Proper job - it had sticky tape holding it down and everything :)
 

Reply to I'm told this is against regulations? in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
516
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
759
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
529
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
590
Hi, I’m new to the forum and am seeking some advice please. I’ve picked up a job that another electrician has abandoned, the job is to...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock