Discuss inspection and testing in the Electricians' Talk area at ElectriciansForums.net

Reaction score
1
evening all,
I am carrying an inspection and test of a board which is located in an area similar to a swimming pool - the board is 40 years old - has no main earth and is reliant on the the conduits connection for earthing- there is no MET within board - all earths are connected to board chassis - there is no rcd protection. The environment is a harsh corrosive environment - some ZS values are high on certain circiuits what is the minimum I can do to get this board to a satisfactory state so that it would pass an EICR.

Cheers
 
It's impossible for any of us to be able to help you without actually being on site.

With regard to "passing" an EICR, only you as the inspector can make that call.

Sorry not to be of more help, but it's just not possible without actually being there.
 
Op You're not going to like most of our replies.
Mine is leave it to someone more experienced, there is no way we can tell you what you need to do, only you as the competent, experienced and qualified inspector can decide that.
Told you, you wouldn't like it.
 
conduits connected to earthing in a corrosive environment is my concern - the board is earthed vi the conduits supplying maintails from isolator below it. I am see the lack on main earth cable as a C1 - and the db should be isolated until the necessary remedial work has been completed

Cheers
 
conduits connected to earthing in a corrosive environment is my concern - the board is earthed vi the conduits supplying maintails from isolator below it. I am see the lack on main earth cable as a C1 - and the db should be isolated until the necessary remedial work has been completed

Cheers

Carry out the EICR then come back with your findings.
 
conduits connected to earthing in a corrosive environment is my concern - the board is earthed vi the conduits supplying maintails from isolator below it. I am see the lack on main earth cable as a C1 - and the db should be isolated until the necessary remedial work has been completed

Cheers

you don't have the authority to cut some ones electric off
 
evening all,
I am carrying an inspection and test of a board which is located in an area similar to a swimming pool - the board is 40 years old - has no main earth and is reliant on the the conduits connection for earthing- there is no MET within board - all earths are connected to board chassis - there is no rcd protection. The environment is a harsh corrosive environment - some ZS values are high on certain circiuits what is the minimum I can do to get this board to a satisfactory state so that it would pass an EICR.

Cheers

Not having a go at you, but are you an electrician, trainee or what?
 
Op You're not going to like most of our replies.
Mine is leave it to someone more experienced, there is no way we can tell you what you need to do, only you as the competent, experienced and qualified inspector can decide that.
Told you, you wouldn't like it.

GMEs I am a competent person dont be rude mate
REread the highlighted text I didn't say you were incompetent
 
Give the customer the EICR that you have deemed as unsatisfactory. Then if the customer wants you to,quote for the work to bring the installation up to a satisfactory condition. Only you know what will be required to make it satisfactory from the codes you have given so everyone on here will be guessing.
 
Input - As stated you/they/someone MUST bring the installation up to standard to get a "satisfactory" EICR
What can you do ?
IF the conduit is not protected against its environment then that could lead to a possible c2/c3 just on containment (Eg if there is reat big rusty holes in it.) If its galv conduit then it should be fine.
What else could you do - Run in cpc's if there are none and run in an earth from the met at the supply. Run in all your usual main protective bonds and assess for the need for supplementary bonding.
As for RCD protection - does it need it in your opinion ? Would the area count as a special location ?
As an inspector you just have to deliver the report imho. Deliver the unsatisfactory report if the install is not up to scratch and quote for remedial works.
You say Zs is high....is it too high ? only you have seen the readings mate.
 
An installation has one MET.
The initials stand for Main Earth Terminal.
An installation may have EMTs (Earth Marhshaling Terminals) as well as a MET, but there is no requirement to such.
All circuits of a location containing a swimming pool, are now (just as with locations containing baths or showers) required to be provided with 30mA RCD protection.
Depending upon where the board is situated, it may be that the circuit supplying the board would also require 30mA RCD protection.
However as the requirements are retrospective, it could be argued that a lack of RCD protection, would only warrent a code C3, if the installation complied at the time of it's design/construction.
 
An installation has one MET.
The initials stand for Main Earth Terminal.
An installation may have EMTs (Earth Marhshaling Terminals) as well as an MET, but there is no requirement to have any.
All circuits of a location containing a swimming pool, are now (just as with locations containing baths or showers) required to be provided with 30mA RCD protection.
Depending upon where the board is situated, it may be that the circuit supplying the board would also require 30mA RCD protection.
However as the requirements are retrospective, it could be argued that a lack of RCD protection, would only Warrent a code C3, if the installation complied at the time of it's design/construction.
I know that mate I was just using the term loosely between sparks lol. This sounds like a sub board to me (so running in an earth from MET would still be "correct" lol). Maybe im just looking too deep into stuff lol.
 
If the board is supplied by steel conduit then it does have an earth, its that steel conduit! There is absoloutely nothing wrong with this and is compliant with the current regulations as long as the connection at each end is electrically and mechanically sound. If it is suffering from a bit of corrosion then the most it might need is a bit of a clean up and some paint to cover the exposed metal.
The same goes for outgoing circuits wired in steel conduit.
 
I didn't reply to your post.
You posted while I was typing.
My comment regarding the MET was aimed at the OP.
He stated that the board doesn't have a MET.
I also suspected that it was a Sub board, which is why I asked for clarification.
Obviously, a Sub board would not have a MET, as the MEt would be at the origin of the installation.
I would expect that there would be a CPC run with the feed to the board, and would expect the CPCs of the circuits fed from this board to be connected to it.
 
Considering it is a swiming fool I would consider RCD protection as a minimum.
and Take a Zs reading (highest reading point) without any touch on main conduits connection point then note it. Would try to make the main conduits connection points better as much it can be.
take a second reading of Zs on same point.
if the second reading comes out with lower reading... report it on EICR with the concerns.
if reading remains same then I would go for Ze.
There would be a better way with someone's opinion.

JD
 
conduits connected to earthing in a corrosive environment is my concern - the board is earthed vi the conduits supplying maintails from isolator below it. I am see the lack on main earth cable as a C1 - and the db should be isolated until the necessary remedial work has been completed

Cheers
Please tell us what gives us the authority to do this. I'd love it if we had the clout but we don't.
 
conduits connected to earthing in a corrosive environment is my concern - the board is earthed vi the conduits supplying maintails from isolator below it. I am see the lack on main earth cable as a C1 - and the db should be isolated until the necessary remedial work has been completed

Cheers

Absence of a suitable means of earthing for the installation is a C2 fella, seeing as there's only any real or immediate danger if a fault occurs

wheres the DB situated out of interest and is there any sign of corrosion to the DB and conduits already?
 
evening all,
I am carrying an inspection and test of a board which is located in an area similar to a swimming pool - the board is 40 years old - has no main earth and is reliant on the the conduits connection for earthing- there is no MET within board - all earths are connected to board chassis - there is no rcd protection. The environment is a harsh corrosive environment - some ZS values are high on certain circiuits what is the minimum I can do to get this board to a satisfactory state so that it would pass an EICR.

Cheers

I think you've had the answers to the more relevant of your questions. The installation sounds as if it's been installed to a pretty high standard for it's day, and as others have stated the conduit IS the CPC, and as the whole installation is metal conduit containment you won't see any separate CPC's unless the board has been added too, with installations that are not in metal conduit containment.

What do you mean by a ''harsh corrosive environment'' and what damage has it caused to this installation?? What do you mean by high Zs values, (you have been asked that a couple of times already but still no feedback)?? What's the Zdb at this fuse board and at the isolator switch below the fuse board?

The older metal fuse boards/isolators etc, didn't come with a means of connecting CPC's as there were none. At the origin of this installation is about the only place you'd actually see a main earthing conductor, and then the chances are it would be a bare conductor connecting to the installations main switch fuse.

The main problem i can see with this sub main, is if any service pipework or structural steel needs main bonding, only you will know the answer to that question. It could well be that all main bonding has been carried out for this building and connected to whatever is being used as the installations MET at the origin of the installation... It may be prudent to check if the sizing of those main bonding conductors are compliant, remembering that they may well be Imperial conductors

On a final note, i personally know of full galv' metal conduit containment systems that haven't been mucked about with, that have been in place 60+ years. The only work that has been carried out on them, being replacing the old VIR wiring and updated fuse boards some 35/40 years ago and not a single CPC conductor to be seen in any of the conduits. I can guarantee that those installations will still be giving Zdb/ Zs values that would impress even the most sceptical among us!!
 
I just cant understand why people get so worked up when steel conduit is used as an earth and no separate earth if you work out the cross sectional earth of a conduit and compare that to say a 1.5 or 2.5 earth or even greater size, there will be no comparison, as long as the conduit is good and sound condition then there's not a problem
 
I just cant understand why people get so worked up when steel conduit is used as an earth and no separate earth if you work out the cross sectional earth of a conduit and compare that to say a 1.5 or 2.5 earth or even greater size, there will be no comparison, as long as the conduit is good and sound condition then there's not a problem

Because they lack a general understanding, knowledge or experience.
Nothing more. Nothing less.:icon12:
 

Reply to inspection and testing in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
720
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
382
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
876
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
767

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock