Discuss Insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Sparky1508, some of the replies you don't like, are probably not helped by the fact, that you do not indicate your qualifications or competency in your profile. You'll see members have gone there to have a look, including me. If you do display them, you might find the negatives a little less shared.

I find fault finding quite taxing, where others on here find it enthralling. As well as the many other helpful suggestions, may I suggest (following safe isolation of course) is removing (not disconnecting) all face plates, too see how many cables you have at each point. This might identify any errant spurs etc, you may not be aware of and indeed might reveal any possible faults, if it is a fault at all.

As davesparks finished his sentence with a comma, you make wish to take up his job offer or mentoring, as he does have a compassionate side which he tries to conceal at times, but indeed has a realm of experience to offer.
 
I was hoping to get help on here as I've seen in many posts he's very knowledgeable and always gives sound advice. I cant seem to find how to put my info on my profile but this is what I now have.
City and guilds 2393-10
City and guilds level 3 2382-15 regs
City and guilds level 3 2394 and 2395
City and guilds 2377-22.
All I want to do is learn that's why I'm on here and at home testing my own stuff before I go out and do it for real.
 
Last edited:
I am not saying that those situations wouldn't cause a fault, i am saying that the test results you have do not indicate that type of fault.

You have made no mention of a dead short in your posts, the lowest resistance I think you have quoted is 0.01M ohms, which is 10,000 ohms, simple maths will tell you that this is will not trip an RCD. A dead short would be in the region of zero ohms.

Nobody knows why they have a low IR reading until they have found the reason, my issue is that you don't understand what the test result actually means in real world terms.
Thanks dave, I realise now what you are saying but I was thinking if a conductor was just very close to another but not actually touching somewhere would that not be similar to having bad insulation or am I still being simple.
 
Thanks dave, I realise now what you are saying but I was thinking if a conductor was just very close to another but not actually touching somewhere would that not be similar to having bad insulation or am I still being simple.

It would have to be very very close for it to have a measureable resistance at 500V.

It would just act as a capacitor
 
Do you have a alarm system connected to the RFC via a spur or a RCD FCU or socket?

Once you start to test in a methodical way as Davesparks as suggested things will become far more clear,I would definately mark the sockets once eliminated dont try and just remember them as you quickly get confused.

Lets hope you tested L/N on soft test on 250 v scale for obvious reasons.

I would suggest access to a tester which has a KOhm range as when testing on the Meg scale when it gives a 0.00 result you need to switch scale to find out exactaly what the reading is. Many MFT testers dont have a KOhm range !


If you get a very low reading then as a guide you can get a rough idea how far away the fault is using maths and cable resistance values!

Let us know how you get on lets hope its not unaccessible joint boxes!
 
Do you have a alarm system connected to the RFC via a spur or a RCD FCU or socket?

Once you start to test in a methodical way as Davesparks as suggested things will become far more clear,I would definately mark the sockets once eliminated dont try and just remember them as you quickly get confused.

Lets hope you tested L/N on soft test on 250 v scale for obvious reasons.

I would suggest access to a tester which has a KOhm range as when testing on the Meg scale when it gives a 0.00 result you need to switch scale to find out exactaly what the reading is. Many MFT testers dont have a KOhm range !


If you get a very low reading then as a guide you can get a rough idea how far away the fault is using maths and cable resistance values!

Let us know how you get on lets hope its not unaccessible joint boxes!
Thanks
No alarm connected.
Will do methodical as Dave suggested.
Forgive me for this but the only reason to test on 250v as far as I am aware is to protect sensitive equipment but I had every plug disconnected from the sockets and had nothing left connected. I know I don't need to unplug but just went round and unplugged everything anyway. Is there another reason I should test on 250v?
 
Last edited:
Thanks
No alarm connected.
Will do methodical as Dave suggested.
Forgive me for this but the only reason to test on 250v as far as I am aware is to protect sensitive equipment but I had every plug disconnected from the sockets and had nothing left connected. I know I don't need to unplug but just went round and unplugged everything anyway. Is there another reason I should test on 250v?

you do this so that, even though you think all loads are disconnected there could be one left that you have missed.
 

Reply to Insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
642
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
505
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
774

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock