Discuss IR test with transformers and dimmer on circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

DaveS

-
Reaction score
24
Evening Chaps

On a job at moment and testing lighting circuits that have a lot of down lighters and a dimmer. Am I correct that if I disconnect live neutral and cpc from board join L-N together with all switches in closed position and test this to cpc and do IR test I have pretty much proved no short circuit between conductors including my switch lines. I will be testing initially at 250v as not to cause damage to dimmer and transformers. Thanks
 
As suggested in previous post the cpc needs to be connected to the means of earthing during an insulation resistance test, so don't disconnect from earthing terminal.
See guidance note 3.
 
Testing at 250 is only acceptable if electronic equipment cannot be reasonably disconnected but I would say in your case a dimmer is easily delt with and 500v can be used.
 
Testing at 250 is only acceptable if electronic equipment cannot be reasonably disconnected but I would say in your case a dimmer is easily delt with and 500v can be used.
The only time I use 250v is when filtered extension leads give false readings and I can't be bothered to unplug them otherwise, 500v all the time and thirty odd years on to my knowledge I have caused no damage.
 
Thanks all very much appreciated especially advice on leaving cpc in earth bar had never considered other cpc's could affect circuit. Always learning
 
The only time I use 250v is when filtered extension leads give false readings and I can't be bothered to unplug them otherwise, 500v all the time and thirty odd years on to my knowledge I have caused no damage.
An Older bloke I worked with used to damage smoke detectors all the time on a 500v test line -neutral.
Must have damaged about 5 houses worth till he realised o_O
 
Last edited:
Older bloke I used to work with used to damage smoke detectors all the time on a 500v test line -neutral.
Must have damaged about 5 houses worth till he realised o_O
Rarely test L/N on periodics unless 100% sure there is nothing across it so that will only be socket circuits
 
Is 500v not likely to damage transformers of down lighters? Also in this scenario for some silly reason all properties have been fed to switches so have atleast 5 neutrals and cpc's at back of box. I am trying to avoid as much any taking off and putting back of switch faces (which would have to do to bypass dimmer) incase I unintentionally cause conductors to become loose. This seems to be the sanest method so far
 
Is 500v not likely to damage transformers of down lighters? Also in this scenario for some silly reason all properties have been fed to switches so have atleast 5 neutrals and cpc's at back of box. I am trying to avoid as much any taking off and putting back of switch faces (which would have to do to bypass dimmer) incase I unintentionally cause conductors to become loose. This seems to be the sanest method so far
Won't cause any damage what so ever.
 
I
Is 500v not likely to damage transformers of down lighters? Also in this scenario for some silly reason all properties have been fed to switches so have atleast 5 neutrals and cpc's at back of box. I am trying to avoid as much any taking off and putting back of switch faces (which would have to do to bypass dimmer) incase I unintentionally cause conductors to become loose. This seems to be the sanest method so far
its becoming common to take a mains down to switches with a neutral as it does away with needing unnecessary junction boxes above ceilings for things like downlights , makes it easier to terminate as well
 
Very true about logic of sometimes wiring to switches but here I really can't see what they was thinking it's a wooden plinth box cut into and can only get depth of shallow back box really with size of dimmer really is hard work getting all conductors at back of box
 
Very true about logic of sometimes wiring to switches but here I really can't see what they was thinking it's a wooden plinth box cut into and can only get depth of shallow back box really with size of dimmer really is hard work getting all conductors at back of box
Yeah 35mm or deeper is sometimes required especially if you've got an in and out mains and a switch wire.
 

Reply to IR test with transformers and dimmer on circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
587
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
633
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
393
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock