Discuss IR Testing??? in the UK Electrical Forum area at ElectriciansForums.net

M

mljc71

Hi All- New to this - loving the challenges!

EICR'd my house and found one of my ring finals had an IR problem- just getting to grips with testing and trying to gain experience- college was good, however, felt like it was more of learning to pass exams!

My ring final has an issue- if i test with breaker open-(off) L(load side of breaker) to E (earth bar) = good reading, N(neutral bar) to E= good reading- but L to N a bad reading. so if a possible dead short between L-N why doesn't breaker trip?

However, if i do a IR L and N to E i get a good result!

Sorry for my inexperience but can anyone help me?
 
What is the result between L/N? You say a dead short, so is the reading 0.00Mohms? Sounds like you may have something still connected like a spur that you may have missed.

Jay
 
Make sure you have disconnected all appliances, especially freezers and fridges. A low Ir reading doesn't mean you have a short.because you are dealing in Mega ohms.
 
nope checked that- has spots in bedroom connected somewhere, but left that part of circuit open,
why a good IR reading with the L-N to E:?
thanks for the reply

lol lots of diy bodges (not mine)! even got an off peak socket! spur'ed off eco10 lol
 
Sounds like a load still connected, neon in a spur or something, could you have a spur in the loft for something if you've got some DIY stuff there.
 
definitely sounds like something still plugged in, did you do end to ends on ring final as had similar when i moved in - one side of ring and immersion heater feed transposed so low ir reading ( imm and ring on 32a mcb and 16a mcb nearly got zapped changing imm stat so did pir and found lots of horrors - funny had just been passed by council contractor)
 
Also the reason you'll have a good reading between both live conductors to earth is because there's obviously no fault to earth hence why it seems like an appliance plugged in because otherwise your ring would trip.
 
ty for replys only 2nd post i think!- will investigate further in loft- also for experience going to take all sockets off and connector block them- do a bell test to check continuity then do IR test- end to end- then cutting circuit into 2 and so on.
 
nope checked that- has spots in bedroom connected somewhere, but left that part of circuit open,
why a good IR reading with the L-N to E:?
thanks for the reply

lol lots of diy bodges (not mine)! even got an off peak socket! spur'ed off eco10 lol
caus your not testing through a load....
 
Because if there was a fault to earth you would have a reading between l+E and or N+E but because there isn't a fault present you will get a good reading, because you're getting a reading between N+L this either means there is a fault but more likely you're getting the reading from a load and the connection between L+N is across the load
 
If your getting a good reading when connecting L&N and testing to Earth then i wouldn't be losing any sleep over it, However as mentioned above the readings defiantly insinuate that something is still plugged in to warrant poor readings. If your L&N to earth is over 1.0 meg then as long as your record how its been tested on the test sheet then that's sufficient.
 
With an IR that low the only conclusion is something is still connected. You have to be very observant doing this job properly or you'll be going round in circles....
 
If you test L to N on low ohms range, what reading do you get? You don't seem to understanding that "0.00Mohms" is not necessarily a "short"; it could be anything up to 10kohms.
 
Found one last week. Extension lighting spurred of through 5 Amp fuse from RFC. Spur behind double bed headboard upstairs.

ALWAYS do 250V test first to find loads not found on visual examination, customer memory/knowledge failure.

I've often found readings in the range of 0.04Mohms for mobile phone/door bell transformers etc... and 0.24-0.26Mohms for neon switches.
 
why L+N to E a good reading? hheellppp want to learn

many thanks all
You say L to E was good, and you say N to E was good, well L and N (connected together) to E is just doing the same test's, you're just doing both at the same time. When you connect L and N together they become one.

Paul.
 
thanks all - found the load in loft- but also e happy with the result i had l+n to e - good to have a bit of reassurance - cheers
also lol on a funny note - or not- what can be done about a neighbours alarm going off-any veiws on the law if i rip out main fuse lmao ! providing no battery back up - ffs lol - spose just call enviromental is best option !!
 

Reply to IR Testing??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
430
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
513
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
690
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
516
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock