Quick query,

When installing a kitchen, is a cooker outlet plate a requirement (recommendation) or could I bring the heat resistant flex from the oven directly into the cooker control unit (45A switch with socket outlet)?

D
 
Quick query,

When installing a kitchen, is a cooker outlet plate a requirement (recommendation) or could I bring the heat resistant flex from the oven directly into the cooker control unit (45A switch with socket outlet)?

D
I don't believe it's a laid down requirement, but normally very good practise. Changing the oven in a few years would become an absolute bugger if it had to be run to the switch, though it may depend on the location of the switch.

If the switch was in a low level cupboard directly beside the oven then perhaps it's less of an issue, but even so the person replacing the oven won't thank you.
 
Hi - not a requirement, but the flex to the cooker will need proper strain relief at the switch (which it gets at the plate ...). There are surface mount back boxes that might be suitable but most of them are intended for small flexes.
 
The cooker switch doesnt include a flex outlet part with cord grip, unless you use a pattress box and a stuffing gland on the flex.

Although, days gone by, ive seen a buried 25mm conduit from the switch with a kick out the wall and the 6mm T&E threaded through.
Dont use T&E now to the cooker of course
 

Reply to Is a cooker outlet plate a requirement? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
1K
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
293
I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
415
A house we have just re-wired has one of these cooker points, Trouble is the kitchen wasn't supposed to have been touched by any trade but...
Replies
6
Views
323
I have a selection of brand new electrical items 6 MK 422. 1g white telephone socket outlets 2 MK 3632. 2g white moulded...
Replies
0
Views
252

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock