Discuss Is this an acceptable means of earthing ? in the UK Electrical Forum area at ElectriciansForums.net

M

Modster

Hello all,

I am doing a consumer unit upgrade for a family member in a domestic household, However i am unsure if ther earthing arrangement is up to scratch, As it is, the main eartghing conductor is clamped onto the incoming supply conduits. Southern electric have been and installed a key meter with the installation as it is, I am jib approved electrician, but im from an industrial background, Any advice from any of you guys would be greatly appreciated. I have attached some photo's for your perusal.

IMG_3771[1].jpg
 
diss those cables from the conduit then try for a Ze. then consider best way to provide a reliable earth, as i bet you won't have one.
 
Current Regs don't support the use of a water gas etc pipe as an earth method. But that looks like the DNO incoming feed conduit.
As suggested I'd test the Ze of just that pipe and see what that gives. I do hope the metals clean under the clamps.
 

Reply to Is this an acceptable means of earthing ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Replies
6
Views
2K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
607

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock