Hi i was looking at this old post and saw a calculation resolved which im not too sure is right and would apprciate confirmation wether it is or isnt

Q24. A continuity of ring final circuit conductors test is to be carried out on a circuit supplying the office. The circuit is wired in 2.5mm cable with 1.5mm cpc. The loop length of the cable is 65m. All socket outlets are connected directly on the ring. Explain in detail, using the information given in figure 1, the three steps required to confirm the continuity of this circuit.
Your explanation should include the
. test instrument
. test connections and the expected readings at each stage
Show all calculations

A24. The test instrument used is a low resistance ohm meter. First test is an end to end of the line neutral and cpc of the ring. This is confirm all conductors form a complete ring. The expected results are:

Line – line – 2.5mm cable = 7.41 mohm/m
(7.41x65)/1000 = 0.48 ohms

Neutral – Neutral – Same as above

Cpc – Cpc – 1.5mm = 12.1 mohms/m
(12.1x65)/1000 = 0.786 ohms

Next cross connect line and neutral of the ring L1 + N2 and L2 +N1 and test at all socket outlets
Expected readings:

R1+Rn = (r1+rn)/4 = (0.48+0.48)/4 = (0.24) ohm Do you use this figure in the stage 3 part of the calculation (0.24)

Next cross connect line and cpc L1 + cpc2 and L2 + cpc1 and test at all socket outlets
Expected readings:

R1+R2 = (r1+r2)/4 = (0.48+0.786)/4 = 0.32 ohms so 0.24 + 0.786/4 = 0.25 ohm ? or do you use (0.48+0.786)/4 = 0.32

Many thanks
James


Read more: http://www.electriciansforums.net/e...1-2391-theory-test-paper-3.html#ixzz2EGbEuDX6
 
hi,
R1+Rn = (r1+rn)/4 = (0.48+0.48)/4 = (0.24) ohm Do you use this figure in the stage 3 part of the calculation (0.24)

(no)

R1+R2 = (r1+r2)/4 = (0.48+0.786)/4 = 0.32 ohms so 0.24 + 0.786/4 = 0.25 ohm ? or do you use (0.48+0.786)/4 = 0.32


you would'nt need to use the expected value of r1+rn (0.24) + cpc (0.78) / 4? if you were looking for your expected R1 + R2 / 4

you could do rn+r2 / 4 or r1+r2 / 4 and get the same result as r1 and rn are the same conductor size and length

hope this helps? :)
 
Last edited:

Reply to Is this calculation correct? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
678
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
616
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
I have been going round in circles with this question. I just cant seem to get an answer remotely close to the options. Continuity of a ring...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock