The SY cable may well be sized correctly for 3 phase but would need to be bigger obviously for single phase as the neutral will be carrying the full current. Did someone already mention this? I'm going a bit senile.....
 
Yes. There was a previous thread about calculating the load, which could have gone like:
'12000/230=52 and 52/3=17.4, check that each element bank is somewhat below 230/17.4=13.5Ω, if so kiln is indeed 12kW as suspected, supply current on single phase is 52A, job done' but rambled on a bit. Somewhere along the way the point surfaced a few times.
 
Last edited:
I find, with SY cable, the size can be surprising. 4mm can look like 2.5, 6.0mm like 4, etc.

Could be because it's flexible.......and not manufactured to any British or European standard, as far as I know.
Isn't it intended as a control cable?.... although 10mm 4c, with such colours as control only, it seems like supply cable. You'd think it would be the all black, numbered cores as controls.
Different manufacturers, different specs, maybe?
 
Or use one on these from RS Components, I have a couple spare if you want one?

Legrand, 4 Pole Interface Module, DIN Rail Mount​


Can't get the link to work, but go to there web site and look for the above, they are a very neat three phase enclosed connector.
 
Or use one on these from RS Components, I have a couple spare if you want one?

Legrand, 4 Pole Interface Module, DIN Rail Mount​


Can't get the link to work, but go to there web site and look for the above, they are a very neat three phase enclosed connector.

They look nice.
 
Although in this case only 2 pole needed, as it's going onto a single phase supply.
 
Usually on dual types of supply like that i.e. three phase/single phase, there is a plate inside the equipment that lets you configure the wiring for single phase supply or three phase, so that you get a two core and earth supply and reconfigure the links inside the appliance rather than try to link one single phase wire to the five core cable. So at your switch you would have a cable coming out from say a rotary isolator straight to the appliance. From there you would have a cable that would go directly to the links. Configuring the links is key to this. Or...three phase rotary isolator and the five core goes into that with a link to each of the L1-L2-L3 at the supply side. I suspect you need to link at where that five core goes to and inspect the arrangement. I have been caught out by this before by assuming the links were configured for three phase and they weren't. So you would need to see how the links are configured and be sure you are linking in properly.
 

Reply to Joining 4 x 10mm conductors? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
663
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I've been volunteering at my local village hall, installing audio and light systems. Converting what was originally an underused sports hall into...
Replies
68
Views
6K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
A customer has asked me to install a supply for a Wenger Webcot kiln. The faceplate is very worn and I cannot see the kW. They state the kiln it...
Replies
60
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock