I have the above 3.0 kVA generator to power a caravan and I am unsure about the earthing requirements. After reading the manual and the HSE guidance I am of the opinion that it is a floating earth and an external earth rod is not necessary. If anyone knows any different or has any advice, it would be much appreciated and most welcome.
 
Hi, welcome to the forum, I have approved this for the general forum until Admin' is online where it may be relocated to the DIY section. This will not effect any postings already made. :)
 
Hi Josh, welcome to the forum.
If you look at page 11 of the manual you will see a section on Generator Use. It states "To prevent electrical shock from faulty appliances, the generator should be grounded. Connect a length of heavy wire between the generator's ground terminal and an external ground source."
Also on page 4 on the section Control Panel you will see a Grounding Terminal.
Hope this helps out a bit.

http://www.kiporpowersystem.eu/DownLoad/2012042608063967.pdf
 
Last edited:
wow... Just realised this was 3 days ago. Better late than never I suppose....
 

Reply to Kipor Sinemaster generator earth in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
528
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hey guys and gals. We bought a small office trailer that is wired up. It's never seen mains power and uses a generator disconnect (220). I read...
Replies
0
Views
1K
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
999
Hi, any help would be greatly appreciated. I’ve been asked to wire up a second hand 3 phase pto generator to an existing generator switch (see...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock