Discuss Lamp Voltage in the UK Electrical Forum area at ElectriciansForums.net

S

Shaun O'Brien

I am currently studying a HNC in building services.
I've been asked to find out typical voltage usage for the following lamps.

Standard Incandescent Lamp
Halogen Incandescent Lamp
Fluorescent Tube
High Pressure Mercury Vapour
High Pressure Sodium
Low Pressure Sodium
Metal Halide
LED

If anyone could give me a list of typical voltage used for these lamps that will be great.

Thanks
 
You say 'Lamp Voltage', are you interested in the voltage at the actual lamp (bulb in UK-speak) or do you want the voltage of the fitting?

There's often a big difference. LED light fittings are often 230vac but the voltage across the actual LED component will be around 3 VDC. Halogen incandescent fittings are almost always 230vac but the actual lamp can often be 12VAC. Same goes for many of the lights you've listed.
 
You say 'Lamp Voltage', are you interested in the voltage at the actual lamp (bulb in UK-speak) or do you want the voltage of the fitting?

There's often a big difference. LED light fittings are often 230vac but the voltage across the actual LED component will be around 3 VDC. Halogen incandescent fittings are almost always 230vac but the actual lamp can often be 12VAC. Same goes for many of the lights you've listed.

I am after the actual lamp voltage, will most of them be 12V? Thanks
 
leds will light up from 1v ... they need a driver to work on 230v.
halogens are mostly 12 or 230.
fluo, hps, metal halide are typically 230v around here, but they are not connected directly, they need a dedicated ballast/control circuit.
standard lamps mostly 230 but they can be 110v too, for use on construction sites etc.
 
I would recommend looking through manufacturers' data sheets, you should be able to get them online for all those lamps and their associated control gear, and you will find all sorts of other useful and interesting information. As they will reveal, some of those lamp types cannot be driven direct with a fixed voltage, the voltage across the lamp being determined by the lamp itself when the driver / ballast passes a regulated current through it. In the UK, control gear for virtually all lamps takes 230V input though.
 
Agree with Lucien, search data on-line as there are lots of variables. LEDs for instance could be 'bare' LEDs or have internal resistors or drivers to allow them to work at 12 or 230V. Even different colour LEDs have a different voltage requirement if they are bare LEDs. Blue are particularly high if I remember correctly. Daz
 
I am currently studying a HNC in building services.
I've been asked to find out typical voltage usage for the following lamps.

Standard Incandescent Lamp
Halogen Incandescent Lamp
Fluorescent Tube
High Pressure Mercury Vapour
High Pressure Sodium
Low Pressure Sodium
Metal Halide
LED

If anyone could give me a list of typical voltage used for these lamps that will be great.

Thanks

Hi dude,the purpose of being asked this question,as part of a HND,is for you to research the types of lamp fittings,individually,and discover the range and type of voltage required.

If you ask for a list of answers,not only will you not guarantee the provenance of that list,you will skip the other bits of information collected along the way.

As with a lot of technical data,the "what",is never as interesting as the "why" :smartass:

Google carbon-arc or HID,and marvel at mans' ingenuity in producing light...

A whole day can be "wasted" merely dissecting and testing the components of a simple florescent assembly,in the course of discovery!

Please do not take this post as undue criticism,but i have recently visited the "Ideal Home Exhibition",here in my fair city,where a gentleman on a stand was attempting to explain the function of a plumbed-in kitchen device...he had all the technical component nomenclature nailed...he even disclosed a HND covering the topic area...but he patently did NOT know how a non-return valve functioned...

Had he dismantled one,and spent a while blowing and sucking through it....he may have avoided embarrassment :rolleyes4:
 
I am currently studying a HNC in building services.
I've been asked to find out typical voltage usage for the following lamps.

Standard Incandescent Lamp
Halogen Incandescent Lamp
Fluorescent Tube
High Pressure Mercury Vapour
High Pressure Sodium
Low Pressure Sodium
Metal Halide
LED

If anyone could give me a list of typical voltage used for these lamps that will be great.

Thanks

I would second the reply saying to do some research.

For example, a metal halide lamp, say an CDM150 will run off a 230V supply with running gear, comprising of a ballast and ignitor. If you're after the supply voltage, it's 230v. However the strike voltage to the lamp will be in the range of 3-5KV with a running voltage of 95v.

I'd say best way is to research typical lamps for each category you are looking at, get the datasheets, and they will give you all the information you need.
 

Reply to Lamp Voltage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
943
I have a question for you all, We recently moved, and the old house had the analog meter on it, the new place has 3 structures on the property.. a...
Replies
10
Views
3K
I am trying to put a 5ft fluorescent light in a garden office on a Dimmable switch. I got standard 230v light fitting which requires a T8 lamp. I...
Replies
7
Views
878
radiohead
R
My parents have a small well house covering a tank and well pump. The house and well house were built in the 1960s and the pump/control panel is...
Replies
1
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock