Discuss LED light in bathroom flashes when extractor fan TP pole switch is closed. in the UK Electrical Forum area at ElectriciansForums.net

But the snubber load will probably work OK though. You could fit it in the isolator, lamp or humidistat, since all have access to SL and N.

One reason we use a snubber (RC network) is that for a given ability to dispose of leakage current, it dissipates less heat when the SL is energised. The capacitor stands most of the 230V, passing a current 230/Xc where Xc is its capacitive reactance. The resistor limits peak currents at sudden changes in voltage e.g. to stop it welding switch contacts. As per the OP, it is possible to use pure resistance instead, but to achieve the same leakage-sinking ability there will be more heat in your back box when live.
 
There's another aspect to using a changeover (2-way) switch to short the lamp which is that L and N are present on N/O and N/C contacts (L1 and L2). In a functional switch that is not designed as an isolator, and made for AC only, the contact separation when open is very small, only a millimetre or two; too small to guarantee that the separation alone will extinguish any arc that forms when a load is switched off. This is deliberate, because the arc will extinguish itself at the next current-zero in the AC cycle and the smaller it is in the meantime, the less heat it will dissipate.
But said switches are rates at 10A, so there could well be a load on the other pole that would sustain an arc of at least 10A when cold, possibly more. So while it is a risk with a historic precident I would be most surprised if any switch rated at 230V/10A was so designed that it could not safely switch from pole to pole without an arc jumping them.
 
In the scenario you describe, if the switch only handles the line, the arc will always be in series with one or other of the loads, limiting its current to within the switch rating. OTOH if L & N are both present on one pole, any arc that forms can transfer to directly between them, bypassing the load resistance, therefore could rise to the short-circuit current.

I agree that very little arc is likely to form in this low-load scenario but if it does, there is nothing to stop it escalating.
 
It's not altogether unlike crossfire in a controlled bridge. Doesn't often happen but can cause immediate destruction if it does. Crossfire can happen in Mercury Arcs too under both controlled and passive rectification. They usually had surge protection across the anodes to minimise the risk of a transient setting it off.
 
Excellent. It's a pity there are so many products that pass the buck as far as compatibility is concerned. You would hope that the makers of the humidistat would acknowledge that low power LED lighting might be connected to the SL and take the necessary (simple) steps to prevent the unit leaking current back out of its control input, and that lighting manufacturers would acknowledge that sometimes the SL gets a bit of inward leakage that should not be allowed to start the lamp. But they are under pressure to squeeze every possible component out of the design to save a few pence, so it becomes a 'system-level' problem to solve.
 
Do you have a multimeter that can measure capacitance? It might be worth checking that the snubber you got is actually working!
Just measured it. It was 95NF so 5% less than it's rated farad which I'm guessing is fine?
 
Yes, mostly they are 10% or even 20% tolerance.
So any thoughts on why the snubber did not work in this case. Would you then need more than 1 snubber or a different rated one?
 
Did the snubber change anything?

Some DC leakage by a controller would not be shunted off by a snubber, so this might just be a reason for it.
 
Did the snubber change anything?

Some DC leakage by a controller would not be shunted off by a snubber, so this might just be a reason for it.
No, it did absolutely nothing. Thanks for all the input pc1966 :)
 

Reply to LED light in bathroom flashes when extractor fan TP pole switch is closed. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
8K
Hi all, wonder if someone can help me. I've bought a bathroom extractor and I do have the wiring there already (previous extractor was there) but...
Replies
6
Views
2K
I'd like to find a timer switch, in a style that looks alright next to decora light switches, to control a bathroom fan. The bathroom fan...
Replies
1
Views
919
Hi, I need to replace an old extractor fan in a house I rent out. The bathroom has a lot of black mould on the ceiling and I'm wanting to prevent...
Replies
5
Views
2K
Hi there. Recently our bathroom extractor fan broke, so I got a new one but I'm having difficulty wiring it (homeowner DIY guy here). So... there...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock