PCD1962

DIY
Reaction score
7
I threw away an old knackered light switch and now need to replace it. It had 4 terminals (L1, L2, L3, L4) and is fed by two blue and two red wires. It has a single rocker.

I assume this is a 1 gang 3 way switch? If not what is it? Where can I get one?
 
It sounds like an intermediate switch but they are normally L1, L1, L2 and L2.
How many switches control the light it is switching.
 
I assume this is a 1 gang 3 way switch? If not what is it? Where can I get one?
As above "Intermediate"
Screwfix! Lots of different ones to choose from, this is the cheapest!
https://www.NoLinkingToThis/p/schne...e-10ax-1-gang-intermediate-switch-white/9869j
 
Thanks both, I’ll give an intermediate a try
At the box where you are replacing the switch, I'd expect one twin cable coming from the hall switch, and another twin coming from the other landing switch.
I'd put one twin cable in the bottom of the switch, and the other in the top, doesn't matter which way round.
Are the conductors of each twin cable really blue and red? I'd expect black and red, or blue and brown! 🤔
 
At the box where you are replacing the switch, I'd expect one twin cable coming from the hall switch, and another twin coming from the other landing switch.
I'd put one twin cable in the bottom of the switch, and the other in the top, doesn't matter which way round.
Are the conductors of each twin cable really blue and red? I'd expect black and red, or blue and brown! 🤔

Could be an old 3 core, with yellow in a connector - hopefully with an earth there too.
 

Reply to Light switch conundrum in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I am trying to replace my old white light switches for nice chrome ones but the wires are all red but the new switch has only l1 l2 top and...
Replies
6
Views
734
Hi all, Looking for someone to help with this dilemma. Image attached to try and explain it better. We have 3 separate lights currently...
Replies
3
Views
658
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
620
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
362
Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
859

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top