TF and the wire

I have to pick up an analogue current 0-20mA from a transducer that converts steam pressure to current, and transfer it over 200 metres to a boiler house, and then convert it back to either 0-10v or 0-20mA or even 4-20mA (trying to find out exactly what they want).

Whats the best way to do it.
 
The distance iisn't an issue but you need to get the customer to define exactly want they want. What kind of input module is to be used, do you need to supply 24V to the pressure switch, if it is 0-20mA ~ 0-10V is easy to convert (500Ohm resistor across the incoming terminal) Otherwise us a signal conditioner etc.
 
Pressure sensors are usually 4-20mA. Does this sensor also come with a transmitter? They usually do. If it's RS485 just run the serial output from this to the boilerhouse.
 
Just a transducer that gives 0mA for 0bar and 20mA for 16 Bar. The boiler people are still fannying around so i just intend getting a 0-20mA signal and let them sort out what they want to do with it.

I don't want it to affect the original measurement displayed on the machine desk. So intend using a signal conditioner.

The distance is more like 300m. Is that a problem.

Anyone give me the finer detail.
 
I've just been reading the spec for an AD converter which may be usefull:

Analog transmitter output, 16-bit, scalable and isolated. User selectable 4-20 mA, 0-20 mA or 0-10V levels. ... The supply can drive 20 mA into a 500 ohm (or lower) load for 10V compliance, or 10V into 5K ohm (or higher) load for 2 mA compliance.

The important point is that the output is conditional on the load resistance. (and the "or lower" bit probably means not less than 200 - 300 ohms, or the device will start malfunctioning)

I would have thought the AD DA solution would have been the best but at 300m the major problem would be pickup on the signal cable. Is it an electrically noisy environment? Intuitivley I would go for the best screened cable I could get and rout it well away from any other electrical cable and preferably in the ground!
 
You need to know if the pressure transducer is loop powered or powered externally.
i.e. loop powered is 2 a wire sensor and is powered by the controllers 4-20mA input.

If its not loop powered the 24volt supply is powered externally of the controller
 

Reply to long distance transfer of analogue signal in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
490
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
794
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top