Hi guys

I was asked by a customer to have a look at a kiln which had failed its PAT test. There's low L-E and N-E insulation readings on the element itself (several coils inside daisy chained together). Readings were about 0.25MOhm so way too high to actually be in contact with the chassis anywhere. I also traced each coil and you can see it's not touching the case anywhere.

As I don't do PAT testing I wondered if anyone knew the acceptable level of leakage allowed to pass and whether there was a way around this so the customer can continue to use the machine?

It seems to me as if this leakage is probably by design (old machine), and the heat insulation inside the kiln is probably ever so slightly conductive.

Any thoughts? I don't to tell them to chuck it as it seems fine, just obviously was designed before some genius came up with PAT testing ............................
 
Hi guys

I was asked by a customer to have a look at a kiln which had failed its PAT test. There's low L-E and N-E insulation readings on the element itself (several coils inside daisy chained together). Readings were about 0.25MOhm so way too high to actually be in contact with the chassis anywhere. I also traced each coil and you can see it's not touching the case anywhere.

As I don't do PAT testing I wondered if anyone knew the acceptable level of leakage allowed to pass and whether there was a way around this so the customer can continue to use the machine?

It seems to me as if this leakage is probably by design (old machine), and the heat insulation inside the kiln is probably ever so slightly conductive.

Any thoughts? I don't to tell them to chuck it as it seems fine, just obviously was designed before some genius came up with PAT testing ............................

I'm no PAT expert but I do recall a minimum IR figure of 0.3MΩ for some heating equipment.

Also remember that mineral insulated elements absorb moisture and if the appliance has not been used for some time, IR readings can suffer.
 
Cheers for that. The element itself is just bare wire coil that sits on the fire proof blocks. I had wondered whether the blocks themselves would absorb moisture as you say and give a reading. Each individual coil gave a reading of about 4MOhm, when all connected in series this obviously drops down to the 0.25.

I wonder if I can tell them to get their PAT tester to do a visual inspection or something as I've checked everything? After testing at temperature first I think to dry it out. As it's a school they're stuck with needing the pointless sticker on the side of it to be able to use it!
 
Cheers for that. The element itself is just bare wire coil that sits on the fire proof blocks. I had wondered whether the blocks themselves would absorb moisture as you say and give a reading. Each individual coil gave a reading of about 4MOhm, when all connected in series this obviously drops down to the 0.25.

I wonder if I can tell them to get their PAT tester to do a visual inspection or something as I've checked everything? After testing at temperature first I think to dry it out. As it's a school they're stuck with needing the pointless sticker on the side of it to be able to use it!

You can recomment that they ask their PAT guy to do a 'touch current measurement'.

This test can be used where you suspect that IR readings are being influenced by something other than a fault.

I'm hoping a PAT expert pops along soon to double check my advice as it's not my particular area of expertise!
 
the 0.3 Mohm is for class 1 heating and cooking equipment not exceeding 3kw all other class 1 should be 1Mohm as normal.

The touch test or "soft test' is highlighted in section 15.6 of the IET code of Practice page 76.

I amaze myself with this PAT lark ...............;);):eek:
 
Do you think that using a "soft test" is likely to give a different result? I see after looking on the net that it can be used on non-IT equipment now but don't have a copy of the code of practice I'm afraid :)

PS The kiln is only small and on a plug top so should be 3KW or less
 
Last edited:
the 0.3 Mohm is for class 1 heating and cooking equipment not exceeding 3kw all other class 1 should be 1Mohm as normal.

The touch test or "soft test' is highlighted in section 15.6 of the IET code of Practice page 76.

I amaze myself with this PAT lark ...............;);):eek:

Lol!

Are you sure it was 'not exceeding 3Kw' I thought it was for appliances 'exceeding' 3Kw?

So if we class a kiln as a heating/cooking appliance which in effect it is, what is the rating of this particular item?
 
I would allow it to warm up a bit then do the test had similar problems with PAT tests. A mate of mine supplies fruit ripening equipment and was getting a lot of equipment returned having failed a PAT test I was asked to look at it and identified humid conditions the equipment is operated in as the problem and damp in the temperature probe as the issue to resolve, when the equipment was put through a short cycle and retested no fault showed up as the probe had dried out.
 
Lol!

Are you sure it was 'not exceeding 3Kw' I thought it was for appliances 'exceeding' 3Kw?

So if we class a kiln as a heating/cooking appliance which in effect it is, what is the rating of this particular item?

Lol so I haven't got this PAT testing lark right lol and that is with the book in front of me ..................:eek::eek:

As the learned man says it is for Class I equipment EXCEEDING 3kw

I shall now go back to my comfort zone and sulk ;)
 

Reply to Low insulation readings on kiln - at what point is acceptable? in the Australia area at ElectriciansForums.net

Similar Threads

Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original...
Replies
6
Views
2K
Been to a fault finding job and lights where tripping the rcbo. After further investigation we found that it was a blue strapper cable (old...
Replies
17
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock