OP
davey_b
What do you mean about the white cable? At the moment that runs to the generation meter, then to an isolator and then to the consumer unit.
Discuss low output until all panels in sun in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
What do you mean about the white cable? At the moment that runs to the generation meter, then to an isolator and then to the consumer unit.
The white cable is way too small it should be 6mm the same as you would use for a shower/ cooker supply.
We had the system installed last September. There was issues with low output and they came back in April and looked at it and output was better. Then I noticed that when it was at peak power it would suddenly drop to 0 and then climb back to nearly 4kw. It was saying "Vac 10 min too high" and "Frequency too high"
The inverter was replaced but now this inverter is saying "Failure fan2" so I'm going to contact solarmax about this tomorrow.
It's a Solormax 4200s inverter and we have 16 Canadian Solar CS6P panels.
As you can see we're getting full sun, it's pretty much straight on the panels and there is a wee bit of shading on the end panels and we're only getting 0.37kw!
DC isolator should be on left side of unit, slightly recessed, not in view on photos.
Yes, that's the one. Would have been amazed if DC isolation had been excluded.
The AC side is somewhat interesting to say the least. The run to the the consumer unit is unlikely to be very long so 4mm T/E would be adequate. Without knowing the rating/sizing of the cable currently fitted it is difficult to comment further. It does however look a little small.
With built in DC isolator not an issue. Start up and shut down procedures must be followed. Like others commenting, I made an assumption about your property from the external shots. At 40m, 4mm cable would not be adequate as the voltage drop would be over 3% where the regs require less than 1%. Therefore 6mm is required.
Please leave everything to a qualified installer.
Reply to low output until all panels in sun in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.