oliver s
I think its hard to say exactly what is causing that as there are a number of issues that need to be sorted as others have said any shading is also a big issue in general it all needs sorting
Discuss low output until all panels in sun in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Yes, that's the one. Would have been amazed if DC isolation had been excluded.
The AC side is somewhat interesting to say the least. The run to the the consumer unit is unlikely to be very long so 4mm T/E would be adequate. Without knowing the rating/sizing of the cable currently fitted it is difficult to comment further. It does however look a little small.
With built in DC isolator not an issue. Start up and shut down procedures must be followed. Like others commenting, I made an assumption about your property from the external shots. At 40m, 4mm cable would not be adequate as the voltage drop would be over 3% where the regs require less than 1%. Therefore 6mm is required.
Please leave everything to a qualified installer.
Hi Davey_b
We are in Edinburgh and would be happy to give you a quote so correct the problems. I know Iain at Tigo so could install optimizers if required, although it may not need it.
Regards
Tom
Cheers.
To be honest if the original installer (they're still trading) doesn't do it as part of the original install I'm going to tell them to come and take it away because at this output I'd be better putting the money in an ISA.
Well, you have had lots of good advice there, but after seeing the pics, and reading all the advice, I do not think that optimisers are the answer for you, In certain circumstances they can be beneficial though.
Firstly, you need to get the two panels out of the shade, either move them or cut the trees, remember that those trees will grow so in 10 years they may shade 4 panels...
It looks like you have space to move 4, just a suggestion.
Also the install needs sorting, that silly bit of flex they have used will/can cause your inverter to go overvoltage, something that some companies do not understand, I think someone did the calcs and said you need 6mm which is always a safe size to use anyway for a domestic install.
I understand your frustration with all of this, but get the system sorted, properly, if it was working as it should you would be over the moon.
My advice would be to let the install company try and sort it, you never know they might have learnt something in a year...
The issue with the trees isn't that they shade all day rather they shade all the panels in the morning and then the panels start to come into sun about 11am and then by 2pm all the panels are in full sun. Thus from my understanding optimisers would help as they would allow us to generate an increasing amount between 11am and 2pm. Sound correct?
Re the white AC cable from the inverter to the generation meter. I measured it this morning and it's 1cm (10mm) in diameter. That's the whole cable including the white insulation. Thus I wonder if the cores are 1.5mm or 2mm at the most? It's a round cable. Thus do you think this is most likely to be the cause of the "Vac 10 min too high" error or "Frequency too high" that was causing the inverter to shut down?
Thanks
Your system as it stands would probably generate more if you removed the 2 shaded panels altogether ( I know thats not the point as you have paid good money for them).
Or if they fitted optimisers at least the panels in sun would be able to generate at full power without being held back by a wee bit of shade.
For the simplest option I would certainly recommend changing the inverter for a SunnyBoy 3600TL.
If you enable OptiTrac (disabled by default) it really does an amazing job dealing with shade.
If you know how the strings are configured then it should be a simple inverter swap.
Ken
We have two arrays here, one with solaredge inverter and optimisers and one with an SMA TL inverter spilt into strings designed to minimise the effect of shading on the array as a whole (i.e one string connected to one of the MPP's gets 'hit' the worst) with optitrac enabled, both get very similar shade. To the annoyance of solar edge, it is very difficult to tell the difference... (there are other technical reasons for installing one of the arrays with solaredge)
Possibly, though you will also want to sort it out into strings that get the worst / best shade / sun.
You should also have a string test doen to see if there are any faulty panels / miss wired strings, your current inverter may have two strings (and one MPP tracker) thouh how have they been physically wired? You want to put all the worst affected panels into just one string, so that will at a minmum mean a good crawl on the roof and look under the panels to see if you can see how they've done it. Most likely it will mean taking at least half the panels off and re-wiring them in the best order. So whilst you've got them off.... what would the cost of optimisers and control box be vs a new inverter...... probably very similar, though the latter may be less actual work.
Aurora Power One have the exact same shading functionality and dual MPPT set up, but for a fair bit less money.Well there we go. It seems that the most straightforward, easiest and cheapest option is fit sma inverter.