Discuss Main bondage in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
17
Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>
 
it is an existing bonding cable, was gonna change the board for an assessment but now i'll need this to be sorted. p.s. the cowboy who installed this bodged quite alot so dunno what is going on
 
Back to your original question does it have to be <0.05ohms......Im not so sure now, I think it is only a recommendation as dont think there is a Reg No but not too sure.....although your reading is very high and is probably due to what Archy has stated
 
There is no limitation on the resistance (or length) of bonding cables, 0.05Ω is just a suggested ball figure (GN3) to prove the cable 'continuity'. However your reading suggests you have a cable of approximately 137m, very unusual in a domestic installation, but never the less, if correct it would conform to BS7671:2008+A1:2011. If this is not the case your test method or connections are faulty and retesting is advisable. In which case if retesting reveals a similar resistance, further investigation and/or replacement would be necessary as it's likely you don't actually have a continuous length of 10mm[SUP]2[/SUP] cable.
 
Last edited by a moderator:
it goes in the floow at front of property, (there are 3 x 10mm and 2x6mm, one 10mm being gas) one resurfaces under the sink and terminated there but i couldnt tell you if it is continuous, i mean why would you not run it continuous whenn the extension was being built!! grind my gears this does.&nbsp;<br>It is maybe 10-15 metre run to the water pipe in kitchen. so it obviously shouldnt be that high....so considered that, it isnt acceptable as the run is so short? or is that 0.05 only ever a rough guide. I mean 0.3 isnt really that bad surely??
 
Between which two points are you measuring to obtain the reading of 0.25 ohms, the measurement of 0.05 ohms is nothing to do with the length of the main bonding conductors as I see it
 
, the measurement of 0.05 ohms is nothing to do with the length of the main bonding conductors as I see it
You are supposed to verify the continuity of the conductor when disconnected so it is all about the csa and length.

A 10mm² copper conductor less than 27m in length cannot be more than 0.05Ω

0.05 is considered negligible - 0.25 or 0.3 is not.
 
it goes in the floow at front of property, (there are 3 x 10mm and 2x6mm, one 10mm being gas) one resurfaces under the sink and terminated there but i couldnt tell you if it is continuous, i mean why would you not run it continuous whenn the extension was being built!! grind my gears this does.&nbsp;<br>It is maybe 10-15 metre run to the water pipe in kitchen. so it obviously shouldnt be that high....so considered that, it isnt acceptable as the run is so short? or is that 0.05 only ever a rough guide. I mean 0.3 isnt really that bad surely??[/QUOTE]

You are joking with this statement I hope...
 
I know that, but that is not how it's explained in GN3 perhaps that's where people get confused with the 0.05 ohms, apparently that is the most common question people get wrong on testing courses. The max resistance value of a main bonding conductor, we all know it depends on the size of the cable and in this case yes with 10mm that equates to a max length of 27m. However the 0.05 ohms in GN3 refers to testing between any two points such as metallic pipes etc That was my reason for asking which two points he was measuring between.
You are supposed to verify the continuity of the conductor when disconnected so it is all about the csa and length.

A 10mm² copper conductor less than 27m in length cannot be more than 0.05Ω

0.05 is considered negligible - 0.25 or 0.3 is not.
 
It's just that the resistance between two points should be negligible so that there is negligible potential difference between them (in the event of a fault).

0.05Ω is deemed to be negligible as nothing will have a resistance of 0.00Ω.

The fact that this equates to 16m with 6mm², 27m with 10mm² or 43m with 16mm² is not really anything to do with it.
(Although, obviously a 10mm² conductor less than 27m cannot be higher than this and in a 'normal sized' property it will be less.)

If the resistance of the pipe itself (without bonding) to the MET and all other pipes and e-c-ps were less than 0.05Ω then the protective bonding conductor would not be necessary.
 
I agree with all you've typed. My asking where he was testing to and from, as in his domestic situation it seemed as though he was using the 0,05 ohms as a guide for his expected reading of his bonding conductor, I didn't realise he was trying to determine the length of the bonding conductor.
It's just that the resistance between two points should be negligible so that there is negligible potential difference between them (in the event of a fault).

0.05Ω is deemed to be negligible as nothing will have a resistance of 0.00Ω.

The fact that this equates to 16m with 6mm², 27m with 10mm² or 43m with 16mm² is not really anything to do with it.
(Although, obviously a 10mm² conductor less than 27m cannot be higher than this and in a 'normal sized' property it will be less.)

If the resistance of the pipe itself (without bonding) to the MET and all other pipes and e-c-ps were less than 0.05Ω then the protective bonding conductor would not be necessary.
 
New posts

Reply to Main bondage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
595
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi I have a 1st fix domestic install on the go and need to leave a socket for other trades to use after me. There is no main bonding at the...
Replies
7
Views
848
I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
407
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock