Discuss Main Bonding Puzzle in the UK Electrical Forum area at ElectriciansForums.net
Thus NO main bonding requiredThere’s no mains gas in the village
Ah if only. As per the essay the incoming LPG supply runs underground in an unidentified fashion before entering the building.Thus NO main bonding required
Again as per the essay this was carried out between MET and LPG/water supplies with main bonding and boiler cpc’s disconnected. Continuity was off scale high to both (>2000 ohm), but IR was 0.00 MOhmYou stated that the water mains is plastic...
Thus NO mains bonding required.
If you still harbours doubts as to whether your incoming services require main bonding you should disconnect the from the MET (by ensuring any cpc, s or bonding clamps etc are removed) and then carry out an IR test between the the incoming service and the MET.
Much, much less. I tried to take your post in, but there's too much there fella. IMO you'll get more help, at least from people with tiny minds like me, if you keep it short and relevant.@Pretty Mouth what other information would you like?
I think it may even not be a fault. Most of these type of situations are, nt. If on a continuity test you get a high resistance, but on an IR test you get 0.00(no resistance,. looks like a short but could really be 10,000 ohms) then it's certainly not a direct contact between a live conductor and a cpc. If it was, a continuity test would pick it up. I would now be looking at the possibility of a DP switch with an indicator light left in the on position.These are the kind of situations that wont show on a continuity test, but will on an IR test. Came across this few times having first (and frustratingly) "ripped" the installation apart.Is this a fixing screw into an earthed metal back box that has grazed the insulation on a live cable type fault, wouldn't be the first time it has happened and left people scratching their head for hours
This wins "tip of the month" as far as I am concerned and could well be in contention for "tip of the year" ?I came up with an idea to use my recently acquired cable tracer and when set up it toned through the fault so into the loft and I followed the tone on the cable to a water tank where the cable was trapped under one of the bearer timbers, tone on one side of the bearer no tone on the other lifted the bearer slightly and the tone disappeared,
Reply to Main Bonding Puzzle in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.