Is this a fixing screw into an earthed metal back box that has grazed the insulation on a live cable type fault, wouldn't be the first time it has happened and left people scratching their head for hours
 
Given the sheer number of bodges and examples of shoddy workmanship from bathroom fitters, kitchen fitters, wet pants and not to mention the DIY electrical works by the previous owner you’re probably spot on.

I suspect when I get the chance to test the pipework just to the external earth the IR reading will improve, but I’ll let you all know when I get around to doing that test.
 
This reminds me of a fire alarm fault I had to deal with around 30 years ago and started my total dislike of FP. This fire alarm developed an earth fault on one zone, an IR test gave very low readings and the continuity readings were over range,
I came up with an idea to use my recently acquired cable tracer and when set up it toned through the fault so into the loft and I followed the tone on the cable to a water tank where the cable was trapped under one of the bearer timbers, tone on one side of the bearer no tone on the other lifted the bearer slightly and the tone disappeared, got the cable from under the bearer did another IR test and got good readings reconnected and tested the alarm and all was good
Since then I have found similar faults in much the same way
 
There’s no mains gas in the village
Thus NO main bonding required

You stated that the water mains is plastic...
Thus NO mains bonding required.

If you still harbours doubts as to whether your incoming services require main bonding you should disconnect the from the MET (by ensuring any cpc, s or bonding clamps etc are removed) and then carry out an IR test between the the incoming service and the MET.
 
Thus NO main bonding required
Ah if only. As per the essay the incoming LPG supply runs underground in an unidentified fashion before entering the building.
You stated that the water mains is plastic...
Thus NO mains bonding required.

If you still harbours doubts as to whether your incoming services require main bonding you should disconnect the from the MET (by ensuring any cpc, s or bonding clamps etc are removed) and then carry out an IR test between the the incoming service and the MET.
Again as per the essay this was carried out between MET and LPG/water supplies with main bonding and boiler cpc’s disconnected. Continuity was off scale high to both (>2000 ohm), but IR was 0.00 MOhm

@Pretty Mouth what other information would you like?

I’ve still not been able to isolate the supply to test just to the external earth, but I did try repeating the continuity tests with my DMM. I know it’s only a low current test, but it consistently reads 3.4 MOhm. IR testing with the MFT still shows 0.00 MOhm, but this time I also paid attention to the voltage. It’s only reaching 6V before displaying 0.00. MOhm.
 
My guess is some metal pipe work, or some related metal back-box, etc, has a bit of corrosion and is in contact with something damp. When you try with a DMM with its 1V or so test voltage you see very high R but pushing a mA or so from the IR tester's 250V+ capable supply whatever layer has formed gives in and conducts.
 
Is this a fixing screw into an earthed metal back box that has grazed the insulation on a live cable type fault, wouldn't be the first time it has happened and left people scratching their head for hours
I think it may even not be a fault. Most of these type of situations are, nt. If on a continuity test you get a high resistance, but on an IR test you get 0.00(no resistance,. looks like a short but could really be 10,000 ohms) then it's certainly not a direct contact between a live conductor and a cpc. If it was, a continuity test would pick it up. I would now be looking at the possibility of a DP switch with an indicator light left in the on position.These are the kind of situations that wont show on a continuity test, but will on an IR test. Came across this few times having first (and frustratingly) "ripped" the installation apart.
 
I came up with an idea to use my recently acquired cable tracer and when set up it toned through the fault so into the loft and I followed the tone on the cable to a water tank where the cable was trapped under one of the bearer timbers, tone on one side of the bearer no tone on the other lifted the bearer slightly and the tone disappeared,
This wins "tip of the month" as far as I am concerned and could well be in contention for "tip of the year" ?
 

Reply to Main Bonding Puzzle in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
880
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
697
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
709

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top