Discuss Main Earth CSA TT Encorporated in a cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
1
Hello All,
Tying my brain in knots trying to work out if this earth is ok:
TT system with 100mA RCD on tails
Tails then go into an isolator with 60A BS1361 fuse which supplies nearby consumer unit and a remote consumer unit in next room.
Remote consumer unit is supplied via twin and earth 10mm (so 4mm CPC - am I right?)
So applying the adiabatic equation to this, my problem is:
Earth rod resistance is 4.05ohm and PFC (to earth) 56A....therefore my 60A fuse is never going to blow so I can't get a 'time' number for the equation.
Obviously the 100mA RCD would trip in the event of an earth fault, but it isn't an RCBO so isn't listed in appendix 3 (time current characteristics) so I'm not sure what to do!

Any help much appreciated :)
 
Hello All,
Tying my brain in knots trying to work out if this earth is ok:
TT system with 100mA RCD on tails
Tails then go into an isolator with 60A BS1361 fuse which supplies nearby consumer unit and a remote consumer unit in next room.
Remote consumer unit is supplied via twin and earth 10mm (so 4mm CPC - am I right?)
So applying the adiabatic equation to this, my problem is:
Earth rod resistance is 4.05ohm and PFC (to earth) 56A....therefore my 60A fuse is never going to blow so I can't get a 'time' number for the equation.
Obviously the 100mA RCD would trip in the event of an earth fault, but it isn't an RCBO so isn't listed in appendix 3 (time current characteristics) so I'm not sure what to do!

Any help much appreciated :)
Did you diss the Main Earth when carrying out your tests?
 
Thats quite a good reading for a TT (4 ohms)
Did you disconnect any possible parallel paths like gas and water if they have protective bonding to them?
Did you carry a out an rcd test on the 100mA rcd?
Not sure what the Adiabatic equation has got to do with anything
 
Last edited:
If your fault current is only 56 amps then t can’t be 1 second.
T is found using the curves from appendix 3 depending on the fault current and the protective device
The rcd is there to give you the fault protection as you can rarely achieve ads on a TT without an rcd.
As the op says 56 amps will never blow a 60 amp fuse
2.5mm can be used on a TT if the cable is protected from corrosion and mechanically protected and not directly buried
 
You have a 100mA RCD to disconnect the circuit in the case of an earth fault. A 100mA RCD must disconnect in 300ms or less at its rated current (100mA).
Since your measured earth fault current is 56A the RCD will (if working correctly) disconnect within 300ms (probably much less).
If you were to use the adiabatic equation with these values the csa would be tiny (0.27mm²), therefore the cpc is suitable for protection against earth fault current.
 
It’s the max time allowed yes but it’s not the figure you would use in the equation.
As I said t would be determined on the fault current
As an example a fault current of 600amps would take 0.4 seconds to disconnect a bs 1361 fuse so if your fault current was 600 amps then t in the equation would be 0.4 seconds regardless of what the max disconnection time is for the circuit
 
You have a 100mA RCD to disconnect the circuit in the case of an earth fault. A 100mA RCD must disconnect in 300ms or less at its rated current (100mA).
Since your measured earth fault current is 56A the RCD will (if working correctly) disconnect within 300ms (probably much less).
If you were to use the adiabatic equation with these values the csa would be tiny (0.27mm²), therefore the cpc is suitable for protection against earth fault current.
It has to disconnect in 300ms however if it was protecting a circuit upto 32 amps on a tt then it must disconnect in 200ms or less for compliance
 
It has to disconnect in 300ms however if it was protecting a circuit upto 32 amps on a tt then it must disconnect in 200ms or less for compliance if non time delayed
The Op example is a distribution circuit protected at 63A.
You would be correct if the circuit was a final circuit and 32A or less.
However most RCDs will trip in far less than the limiting time and the actual trip time recorded, even if only at 100mA, could be used as a worst case scenario where the fault was not of negligible impedance. Since the trip time at a higher current will not be less than the recorded time.
 
we also have PEFC.....

Professional Electrician Football Club.
 
not to be confused with PNEFC

Prospective Neutral/Earth Fault Current, or Preston North End FC.
 

Reply to Main Earth CSA TT Encorporated in a cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
239
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
702
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock