Discuss Main gas bond connected in the wrong place in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
92
hello guys

I need some advice on and EICR job.
On the MET we have two main bonding conductors 10mm each.
Water is fine however I cannot find the gas bond connection on the pipe.
I know it is connected to the pipe as a long lead test gives me 0.02.
The pipes resistance rises as I disconnect the main bond and clamp between the met and gas pipe.
What would you guys advise as I cannot see the connection within 600mm of the Pipe.
Code 3 advise having the bond reinstalled?
 
Did you disconnect both ends i.e. From the MET as well?
If still connected you may pick up parallel paths from say a cpc connected to the boiler through the gas pipe from the central heating circuit for example.

Sorry re read it yes you did! o_O
 
That would make the overall assessment unsatisfactory.
I'm not sure it deserves that.
The way I view it is if you're there to do an EICR, you're not there to tear the house apart to do so, in all probability you've given them a fixed price for the EICR which would cover basic, reasonable, investigative actions you'd need to take in order to complete the EICR. If you can't because of e.g. this situation then it comes under additional work/cost required and is explained/justified by the FI code.
 

Reply to Main gas bond connected in the wrong place in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
2K
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock