cliffed

-
Arms
Supporter
Reaction score
645
We have tables for the correct sizing of earth conductors & MPBC.
We can also size cpc’s by calculation,can we actually calculate for MPBC.
 
with PME it's got to be 10mm. otherwise caclulate. with TN-S 6.0mm usually suffices. with TT, a piece of wet string.
 
Actually main protective bonding conductors cannot be calculated.
544.1.1 except for PME, a main protective bonding conductor shall be not less than half that of the earthing conductor and not less than 6mm.
The same would apply to TT.
 
Actually main protective bonding conductors cannot be calculated.
544.1.1 except for PME, a main protective bonding conductor shall be not less than half that of the earthing conductor and not less than 6mm.
The same would apply to TT.
Yea thought that,have a look
 

Attachments

  • 86C9E683-2644-4609-970F-96A54EBBA906.png
    1.8 MB · Views: 19
You also need the max I2t for the main OCPD (probably from 5s disconnect BS88 fuse, but not always as MCCB let-though could be higher at max PFC in some cases).

Usually it is simpler just to go with the Table 54.7 values to get the main earth size, and allow for any PME limits from Table 54.8 but for most cases it will be easier just to stock 10mm!
 
You also need the max I2t for the main OCPD (probably from 5s disconnect BS88 fuse, but not always as MCCB let-though could be higher at max PFC in some cases).
A quick check for typical main OCPD shows:
  • 100A BS88-5 fuse is about 580A at 5 seconds so 1.7MA for I2t leading to 11.3mm for 70C thermoplastic k=115, or 7.4mm for k=176 (separate protective conductor 90C thermosetting)
  • Hager 100A MCCB is worst-case just before magnetic trip with I2t around 13MA (from catalogue page 127 graph) leading 31.3mm for k=115, or 20.5mm for k=176
Hence the MCCB needs about 2.7 times the CPC size.

Both MCCB calculated values are above the Table 54.7 sizes for main earth (typically 100A would be 25-35mm line so 16mm CPC there). Halving for 544.1.1 protective bond sizes gives:
  • 100A BS88 fuse 5.7mm or 3.7mm => 6mm minimum
  • 100A MCCB 15.7mm or 10.3mm => 16mm minimum
 
Last edited:
sooo, basically, it's half the size of the MEC (not necessarily in the right order, oops, or calculate the min.required for MEC and go fer half of that).
 

Reply to Main protective bonding conductors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
692
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
531
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
305

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock