Useful tip, if you join your local library you should get an online account. As well as being able to read books and magazines online, you should get access to British Standards Online and you can get the fire regs there.

For those who can't be bothered to sign up with their library, Drop me a PM - if you're a long standing member on here who I have built up a trust for, I may be able to help you out.
 
The cable is cover by both BS5839 part 1 and BS7671, and should be tested and recorded as any other cable installed. This also goes for zone/loop cables and any bell/sounder cables.
 

Reply to Main supply to fire alarm panel in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am doing renovation to a cafe in Scotland at the moment and after speaking to the local council the building requires the minimum standard for a...
Replies
5
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
643
Hi guys been asked to put a radial in for spurs for a fire alarm panel supply is it okay to use red FP200 to carry 230v? If so or not could you...
Replies
11
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Been having issues with a pair of linked Actulux SVM controllers. If the fire alarm is triggered the controllers show 'Alarm' and the AOVs open...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock