Discuss main switch question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
20
Hi guys,

Im installing some main switches in an installation to cover 3 boards.

A question i have is, they anything against the regulations or indeed bad practice to fit a single main isolator switch to cover the 3 boards or should they have 3 individual ones.

What i got is a single phase load coming out main supply into a henly block which then feeds 3 DBs. Should it be okay to pick the incoming feeds into the henly block and take then into isolator and then new meter tails from isolator back into the henly block which would then feed the 3 dbs. So basically putting the main switch before the henly block?

obv this is the cheaper and quicker solution, but i just want to make sure im not missing anything which makes this against the regulations?

thanks in advance
 
I havnt actually seen the installation, yet so got limited info. On a pic i seen the other day it looks like BD1 and BD2 are main switches feeding boards else were in the building so it might just be a case of the main switch is only needed for DB3.

However if thats not the case then the other 2 boards only very small. maybe a one way and and 3 way. not sure what they feeding as of yet.
 
I havnt actually seen the installation, yet so got limited info. On a pic i seen the other day it looks like BD1 and BD2 are main switches feeding boards else were in the building so it might just be a case of the main switch is only needed for DB3.

However if thats not the case then the other 2 boards only very small. maybe a one way and and 3 way. not sure what they feeding as of yet.

I'd be going to have a look!
 
posts #4 and #5 are your best advice.
 
install a board and feed the others off this, much neater.

But not necessarily the right answer, depending on the type of board used the main switch may not be suitably rated for the switching duty or it may not be possible to achieve discrimination in the protection.

There has been no mention of the size of the incomer or main switch or the nature of the installation. It could be an 800A TP supply for all we know
 
But not necessarily the right answer, depending on the type of board used the main switch may not be suitably rated for the switching duty or it may not be possible to achieve discrimination in the protection.

There has been no mention of the size of the incomer or main switch or the nature of the installation. It could be an 800A TP supply for all we know
???? a main switch doesn't trip,

its a single phase supply i would be surprised if its over 100amp because above this i would have thought it would be 3 phase.

how would discrimination be a problem if 3 mcbs feeding 3 sub boards?

if thats true then every large building in the country has been wired wrong.


thats one big henley block for 800amps then lol.

busbar chamber with isolator for each if thats the case then
 
???? a main switch doesn't trip,

its a single phase supply i would be surprised if its over 100amp because above this i would have thought it would be 3 phase.

how would discrimination be a problem if 3 mcbs feeding 3 sub boards?

if thats true then every large building in the country has been wired wrong.


thats one big henley block for 800amps then lol.

busbar chamber with isolator for each if thats the case then

I didn't say anything about the main switch tripping, I mentioned switching duty which is the type of load it is able to switch. If the load is highly inductive it needs a different switching duty to a standard DB main switch.

I'm sure he said earlier that the 2 pole isolator suggested was no good as he had a three phase supply.

Discrimination will be a problem if the tripping curve of the sub main MCB overlaps that of the final circuit MCB in the sub DB. Discrimination is concerned with ensuring that under fault conditions the final circuit protection will operate before the distribution circuit protection. This is one of the reasons HRC fuses or MCCBs are preferable for submains.

Yes I missed the bit about the Henley blocks, that suggests it's going to be no bigger than 200A
 
I didn't say anything about the main switch tripping, I mentioned switching duty which is the type of load it is able to switch. If the load is highly inductive it needs a different switching duty to a standard DB main switch.

I'm sure he said earlier that the 2 pole isolator suggested was no good as he had a three phase supply.

Discrimination will be a problem if the tripping curve of the sub main MCB overlaps that of the final circuit MCB in the sub DB. Discrimination is concerned with ensuring that under fault conditions the final circuit protection will operate before the distribution circuit protection. This is one of the reasons HRC fuses or MCCBs are preferable for submains.

Yes I missed the bit about the Henley blocks, that suggests it's going to be no bigger than 200A
fair enough but im sure you can still buy bs88 boards.

or mccb's
 
how would discrimination be a problem if 3 mcbs feeding 3 sub boards?

An MCB feeding a distribution circuit for a dis board with MCBs on it is nearly always going to suffer from a lack of discrimination/selectivity. Cascading MCB discrimination is nearly impossible to achieve.
 
An MCB feeding a distribution circuit for a dis board with MCBs on it is nearly always going to suffer from a lack of discrimination/selectivity. Cascading MCB discrimination is nearly impossible to achieve.
an mccb main switch then mcb's or mccb's feeding sub boards.

when the shower/sockets/lights trip it doesnt trip every other mcb does it, same thing
 
an mccb main switch then mcb's or mccb's feeding sub boards.

when the shower/sockets/lights trip it doesnt trip every other mcb does it, same thing

Depends on the magnitude of the fault on the sub-DB circuit Shanky, with MCBs you only get partial discrimination at best, as Davesparks pointed out earlier HRC fuses > MCBs provide better discrimination.
 
Depends on the magnitude of the fault on the sub-DB circuit Shanky, with MCBs you only get partial discrimination at best, as Davesparks pointed out earlier HRC fuses > MCBs provide better discrimination.





Depends on the magnitude of the fault on the sub-DB circuit Shanky, with MCBs you only get partial discrimination at best, as Davesparks pointed out earlier HRC fuses > MCBs provide better discrimination.
what im saying though is the intake would be into a mainswitch that wouldnt trip then wither mcb's,mccb's idealy for each board.

they are all split off from the same point so how can the others trip honestly.

if the supply to all three was fed from the same mcb etc i could understand where you are coming from
 
what im saying though is the intake would be into a mainswitch that wouldnt trip then wither mcb's,mccb's idealy for each board.

they are all split off from the same point so how can the others trip honestly.

if the supply to all three was fed from the same mcb etc i could understand where you are coming from

I agree with you here ^^, I thought you were talking about feeding the sub-boards from an MCB, my bad :35: lol
 
an mccb main switch then mcb's or mccb's feeding sub boards.

when the shower/sockets/lights trip it doesnt trip every other mcb does it, same thing

No it's not the same thing, you suggested installing a DB and feeding sub mains from MCBs in that DB.
That puts the final circuit MCBs on series with the distribution circuit MCB, this will may not discriminate in the event of a fault on the final circuit.
 
No it's not the same thing, you suggested installing a DB and feeding sub mains from MCBs in that DB.
That puts the final circuit MCBs on series with the distribution circuit MCB, this will may not discriminate in the event of a fault on the final circuit.

That is what I thought I was replying to earlier, tis Friday night though ;)
 
the installation is a 3 phase incoming, however only one the phases used which goes into a henly block then splits into 3.

so best practise would be to place the isolator before the henly block so the main switch covers the whole installtion.

oh and they reasons why the main switch cant be a RCD switch.
 
the installation is a 3 phase incoming, however only one the phases used which goes into a henly block then splits into 3.

so best practise would be to place the isolator before the henly block so the main switch covers the whole installtion.

oh and they reasons why the main switch cant be a RCD switch.

Do you really need to ask this??
 
Read 314.1 in the BGB then have a think why you shouldn't fit a RCD main switch on a TN system.

potentially if we had nuisance triping it could be a killer for this type of business. so rcd protection as a main switch is a no no. RCBO protection for socket circuits is needed so only that circuit in question would disconnect instead of whole supply
 
There is no requirement for RCD protection of socket circuits, unless the installation is considered a special location.
Just wondering whether the meter is single or 3 phase?
 
Good luck with that.
89be3fe547f7827761cd8a9a968ab80a.jpg


4aa244d888ed7955087e3fc4173c1dac.jpg
 
Thanks for that, as you can see from what you have quoted, there is no requirement for the circuit to be provided with RCD protection.

Socket-outlets are required to be provided with RCD protection, not the circuits supplying them, except in some instances where the installation is considered to be a special location, such as Horticultural or Agricultural.
In fact providing RCD protection for such circuits could be a non-compliance in some circumstances.
 
Socket-outlets are required to be provided with RCD protection, not the circuits supplying them, except in some instances where the installation is considered to be a special location, such as Horticultural or Agricultural.
In fact providing RCD protection for such circuits could be a non-compliance in some circumstances.
if the cable is not more than 50mm in wall or has mechanical protection then it needs an rcd
 
if the cable is not more than 50mm in wall or has mechanical protection then it needs an rcd
Still no requirement for socket circuits to be provided with RCD protection.
Yes there are circumstances where it may be advisable, or the simplest solution to provide RCD protection for such a circuit.
However it still remains that there is no requirement in BS7671 for such circuits to be provided with RCD protection, except in some circumstances where the installation is considered to be a special location.
Doesn't matter whether there is a dwelling involved or not.
 
Still no requirement for socket circuits to be provided with RCD protection.
Yes there are circumstances where it may be advisable, or the simplest solution to provide RCD protection for such a circuit.
However it still remains that there is no requirement in BS7671 for such circuits to be provided with RCD protection, except in some circumstances where the installation is considered to be a special location.
Doesn't matter whether there is a dwelling involved or not.

411.3.3

Addition Protection RCD

Socket outlets not exceeding 20 A
 
The difference is the regulations say socket outlet and not circuit. For example you could have the circuit installed surface so doesn't require RCD protection but you would install a RCD socket outlet to comply.
 
No, it came into effect on the 1st Jan 2015 but the 'old' regs don't cease until the 30th June 2015 so the 3rd amendment is actually Currently in effect.

It was published on 1st January, with an effective date of 1st July. So BS 7671:2008 (2013) is still current.
 
No, it came into effect on the 1st Jan 2015 but the 'old' regs don't cease until the 30th June 2015 so the 3rd amendment is actually Currently in effect.

Wrong! this is of the IET website;


Amendment No. 3 to BS 7671 Wiring Regulations will be published on 5 January 2015, and will come into effect on 1 July 2015. The new reference for the book will be ‘BS 7671:2008+A3:2015’.
All new installations must comply with BS 7671:2008+A3:2015 from 1 July 2015.
In this update, a number of potentially life-saving changes have been proposed, which include, but are not limited to, changes to:
consumer unit enclosures (to come into effect January 2016);
wiring in escape routes;
changes to earth fault loop impedances for all protective devices;
the risk assessment approach for the omission of RCDs in non-domestic situations;
updated EIC and EICR forms; and
changes to definitions throughout the Wiring Regulations.
 

Reply to main switch question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
486
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
747
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock