I can't find anything in the regs. On a ring it's fine to run a spur from the MCB (so 3x2.5mm). On a radial technically it doesn't matter where connections are made to the circuit as long as the cable at any given position can withstand the load. So how many connections from the MCB would be acceptable? Would you go by manufacturer's recommendation as to how many the terminal can hold?

I have to add 2 sockets into a radial run (currently a mix of 2.5mm & 4mm single cores and T&E on a 20A type C MCB). I could break into the main leg of the radial from a steel conduit inspection bend and leave a wago box hanging out of the bend (a bit messy IMO, even though hidden above a ceiling), but it's only about 6 feet further to the board so I'm thinking of just coming off the MCB instead. There are currently 2 connections in the MCB and it got me wondering how many you could technically fit.

And before anyone asks, this radial is the only RCBO on the board so I want to come off this circuit to save spending £100 on a Merlin Gerin RCBO just to put 2 sockets in.

Let the arguments commence.............................. :)
 
hmm tricky one this, i have installed 3 radials from a MCB before for different lights, i assume as long as you have a decent connection and you do not stress the MCB retaining screw then as many as you deem practical. (obviously IAW Manufactures installation instructions) and don't over load the MCB!
 
yes im waiting with baited breath for the replies on this. Tried to find a similar answer some time ago and never reallly came up with an answer i was happy with..!
 
Phone up your Part P scheme provider and let them earn their money.Then that way if it gets pulled for assessment..hey presto it was them that advised you :D.

Let us know what they said though.....
 
have a read at reg 523.8 conductors in parallel. in my opinion 1 cable at mcb.
 
Last edited:
I agree with above apart from anything else how much power would the client lose in the event of a trip of the MCB.


Chris
 
I would teat as a spur so never more than two at mcb although nothing wrong with radiating out from source like spokes of wheel except for space constraints
 
Have been picked up on this by one of my fellow testers:eek:. Sintra is correct I believe, only one connection at an MCB except on a ring/spur arrangement (which seems backward to say the least).
On a practical level, I would have no problem with seeing two cables in an MCB , as long as ccc's are considered, and they are serving similar circuits i.e. two socket radials, two lighting circuits etc.

Would be intersted to know if you'd get pulled for it by your inspector?
 
Other than saying, it should be only one wire at the mcb
I would be interested to hear the safety reasons why people think it cannot be more

If I was wiring a lighting radial and the lighting was in two opposite directions from the mains board,I would have no hesitation whatsoever taking 2 or more cables from the same mcb

In the above situation,I would say it is not only permissable,but a safer install because of the lower Zs that the branches would give, compared to a run which is doubling back on itself, just to please some obscure reason abot core numbers in an mcb
 

Reply to Maximum number of conductors in MCB for radial circuit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
309
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
676
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
855
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
884
Hi, I`m looking for an advice. I have an electric shower that I`m not using due to boiler changed to combi and added shower over bath feed by a...
Replies
1
Views
944

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock