Search the forum,

Discuss Maximum Number of electric showers!?! Help in the UK Electrical Forum area at ElectriciansForums.net

W

Will Mcloughlin

Hi guys
Basicly iv got a 6 bedroom house
100A bs 1361 single phase supply
main fuse board is new with 25mm tails with 2 spare ways
would a extra submain fed by 25mm tails for the origin support 5 shower circuits say 40A MCBs 10mm cables 8KW showers
taking into consideration diversity would this be acceptable?
Cheers
Will
 
ridiculous. rethink the job for power showers. heat water with gas.
 
Ludicrous. Even having two electric showers is pushing it really. Are there really that many dirty people in your house, anyway? When I moved into my current house, the toilet was still in the cellar. If I wanted a shower I had to stand in the loft and wait for it to rain!
 
Ludicrous. Even having two electric showers is pushing it really. Are there really that many dirty people in your house, anyway? When I moved into my current house, the toilet was still in the cellar. If I wanted a shower I had to stand in the loft and wait for it to rain!

A toilet in the cellar??

WOW!!! ..... what luxury!

Ours was at the bottom of the yard and wasn't of the flushing type which were for folk like bank managers and vicars - it was emptied with a shovel about twice a week.

Lighting was by candle so we had no arguments about supplementary bonding .....................
 
Hi guys
Basicly iv got a 6 bedroom house
100A bs 1361 single phase supply
main fuse board is new with 25mm tails with 2 spare ways
would a extra submain fed by 25mm tails for the origin support 5 shower circuits say 40A MCBs 10mm cables 8KW showers
taking into consideration diversity would this be acceptable?
Cheers
Will

Ask the customer to request the DNO to provide a 3 phase 150A supply to the premisses, that should see you alright!! lol!!
 
5 showers in one house?? This must be flats/student digs?? Daz
 
There seems to be a trend these days for how many bathrooms a house can have. People seem to want to outdo their friends. Just seems like a lot more expense and a lot more cleaning to me. Daz
 
There seems to be a trend these days for how many bathrooms a house can have. People seem to want to outdo their friends. Just seems like a lot more expense and a lot more cleaning to me. Daz

I think the more bathrooms, the more your house is worth, hence if you convet every room in your house into a bathroom or an ensuit bathroom (but get rid of the bedroom so its ensuit to a bathroom) you'll be incredibly wealthy or at least have some where to ****
 

Reply to Maximum Number of electric showers!?! Help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm converting my old garage into a two bedroom annex. At its nearest point it is approx 10m from main house. I plan it to be all electric, UFH...
Replies
5
Views
3K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
537
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K
Long time lurker so this may be my first question. I am a qualified electrical engineer, but in aeronautics not domestic installations, and I may...
Replies
21
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock