Don't know if any one can help here. Today whilst doing a Zs test my megger produced a weird symbol that looked a bit like a sine wave with a vertical line dissecting it at the top. It have the correct Zs result at the same time. But id never seen the symbol before
Can't find anything about it in the instruction manual.
 
i'm not sure, but i would agree with topquark. dammn, that'as twice in a week. LOL. :13:
 
contentious later? sounds like a tribute band for tenacious D.
 
It was in a school, the reading was on a ring and was exactly what I was expecting. Just that this symbol came up and earlier that day, on a different circuit, on a different board (but in the same building) the fuse went in my meter. Coincidence maybe?

The wiring is pretty old school, as is the protection lots puff beneath. Most of the boards in the building are isolated -10 or so.
 
It was in a school, the reading was on a ring and was exactly what I was expecting. Just that this symbol came up and earlier that day, on a different circuit, on a different board (but in the same building) the fuse went in my meter. Coincidence maybe?

The wiring is pretty old school, as is the protection lots puff beneath. Most of the boards in the building are isolated -10 or so.

Sorry - predictive text went mad on me then - i meant to say lots of bs88 fuses - not lots of puff beneath !
 
If i remember correctly , this is what my megger used to show when it went up s""t creek ?
Each time was followed by a rather expensive repair and get this ! The need to pay for a recalibration as megger would not do it at the same time as the repair ???
It happened 3 times in one year about 5 years ago and thats when i went for a top line fluke and touch wood to date !!!
 
Had my 1552 for over 4 years. It has displayed that symbol maybe 3 times.

It did not go ---- up immediately after.


It would be nice if a megger chap gave a thorough detailed explanation of what this symbol means?
 
Had my 1552 for over 4 years. It has displayed that symbol maybe 3 times.

It did not go ---- up immediately after.


It would be nice if a megger chap gave a thorough detailed explanation of what this symbol means?

It may of been another symbol that used to appear , it has been 5 years since i have used a megger !
It should still be in the stores where it got placed in disgust , i suppose i should send it off again and get it sorted as a spare .
 
Had my 1552 for over 4 years. It has displayed that symbol maybe 3 times.

It did not go ---- up immediately after.


It would be nice if a megger chap gave a thorough detailed explanation of what this symbol means?

Yea right, it must be a feature of the model. Whatever it is trying to tell us.
 
It may of been another symbol that used to appear , it has been 5 years since i have used a megger !
It should still be in the stores where it got placed in disgust , i suppose i should send it off again and get it sorted as a spare .

i'll buy it if the price is right, i love megger gear.
 
i'll buy it if the price is right, i love megger gear.

Off on holiday in the morn for a week , if i remember i will have a look for it when i go back down to Bucks and i am at the stores again .
It will probably around the 5th Sept , so feel free to pm me and remind me around then .
 
dp, i'm 65. how in hell do you expect me to remember as far away as after tomorrow?
 
actually, after tomorrow was being optimistic. i'm lucky to remember after the next pint.
 
Had my 1552 for over 4 years. It has displayed that symbol maybe 3 times.

It did not go ---- up immediately after.


It would be nice if a megger chap gave a thorough detailed explanation of what this symbol means?

The noise warning symbol is a sine-wave with a spike on the positive half cycle, seen at the top of the display just right of centre on an Megger MFT 15xx.

The noise warning symbol on a Megger MFT 15xx, 17xx or 18xx is very rare event, due to the multi-pulse, noise cancellation measurement method employed. It is because of this patented technique that the Megger MFTs gets unfair criticism from users of other MFTs (Fluke devotees in particular) for it's apparently slow "No-trip" test, however, Megger users get the last laugh because they very rarely have their test inhibited by a noise error whereas Fluke users see their equivalent, Error 5, fairly regularly even in the domestic environment. Most Megger users reckon on it occurring about once a year, maybe a few more if you do lot of industrial work, and usually on a No-Trip loop test.

The noise warning symbol is displayed when there is excessive noise on the supply. Noise or transients on the supply voltage can effect the accuracy of the loop measurement during the test and introduce an error in the reading. The noise or transient on the supply voltage are usually caused by active appliances or equipment on the supply, the source usually this internal to the installation, but equally may be caused by an external source. Internal sources can usually be isolated (switched OFF) eg. automatically switched loads and motor controllers, however, when external sources are the cause it may require testing at a different time of day to avoid the active period, during their lunch hour or after normal working hours eg. A garage down the road maybe using welding equipment or the Vets /Doctors surgery using X-ray equipment.

If the noise warning symbol is displayed the reading should be treated as in-accurate and the test repeated, usually a second test is all that is required to get a reliable reading. If the noise symbol continually appears on repeated test the cause should be investigated.
[FONT=&amp]In an industrial environment where continuous production must be maintained and the noise source cannot be isolated, often the only thing you can do in the short-term is to take a series of readings and record the average value to minimise the error.

[/FONT]
 
Last edited by a moderator:
If i remember correctly , this is what my megger used to show when it went up s""t creek ?
Each time was followed by a rather expensive repair and get this ! The need to pay for a recalibration as megger would not do it at the same time as the repair ???
It happened 3 times in one year about 5 years ago and thats when i went for a top line fluke and touch wood to date !!!

This type of behaviour is typical of a faulty Megger MFT continually displaying the hot warning symbol, when Hi-current loop testing, despite ensuring the MFT has cooled down between tests. Usually caused by a loop load that has reduced in value outside the manufactured tolerance and is being 'cooked'.
The hot warning symbol is a 'thermometer' seen at the top of the display on the far right hand side, on a Megger MFT15xx.
Because the repair of this type of fault requires the replacement of a number of components parts the instrument inevitably requires adjustment and re-calibration to ensure its intended accuracy is brought within the manufacturer's original specification.
 
Last edited by a moderator:
323.jpg322.jpg321.jpg320.jpg319.jpg318.jpg324.jpg


Hi Telectrix , i know it has taken about 8 months but here it is !
It has been in a flight case on a shelf in the stores for the last 6 years or so after it played up last time .
 

Reply to megger 1552 sine wave symbol in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Please help, I'm still new to testing for myself and sometimes I wonder if my new Megger is being naughty on purpose as my Fluke wasn't as prone...
Replies
27
Views
5K
M
Hi, Borrowed someones megger 1552 today to megger an alternator @ 1kv and check windings. now keeps showing battery symbol on IR test It was...
Replies
4
Views
3K
MacLec
M
S
Hi tried to do a Zs at a house today and my meter displayed "fus" NEVER seen this before. Not in the manual. Not the fuse symbol...
Replies
4
Views
3K
SPARTYKUS
S
R
Hello all, I am after some advice, I have just bought a megger 1552 tester. I was "practicing" with it today as I am a novice when it come to...
Replies
11
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock