Discuss Melted Plug and Socket cause in the UK Electrical Forum area at ElectriciansForums.net

Hi all,
Washing machine plug and socket melted around Neutral pin. Whilst removing socket faceplate, noticed one brown wire was not in the terminal. May have come out of the terminal when pulling the socket forward or may have been out all the time.
Is this lose or disconnected live cable the 'definate' cause of the overheating on the neutral pin?
Thanks, Gary

Hi Gary

Had the brown (Live) wire not been present you wouldn't have got much washing done ?.

The fact that it came out when withdrawing the front plate definitely indicates it wasn't tightened properly in the first place, and you have a cr@p installation.

So long as the wires aren't burned back beyond trimming distance this is no big deal. Just buy a decent quality new socket and replace it. Ditto a decent plug for the flex.

It might be worth gradually going round all your other sockets to check terminal tightness as well (switch off at the board first!). There's a bit of craft in getting the torque right - it should be firm, but not torqued down like the wheel nuts on a 44 ton truck! All that does is to strip the threads and/or cut through the copper cable.

Cheers and good luck, Mark.
 
Thanks all
Hi Gary

Had the brown (Live) wire not been present you wouldn't have got much washing done ?.

The fact that it came out when withdrawing the front plate definitely indicates it wasn't tightened properly in the first place, and you have a cr@p installation.

So long as the wires aren't burned back beyond trimming distance this is no big deal. Just buy a decent quality new socket and replace it. Ditto a decent plug for the flex.

It might be worth gradually going round all your other sockets to check terminal tightness as well (switch off at the board first!). There's a bit of craft in getting the torque right - it should be firm, but not torqued down like the wheel nuts on a 44 ton truck! All that does is to strip the threads and/or cut through the copper cable.

Cheers and good luck, Mark.

Hi Gary

Had the brown (Live) wire not been present you wouldn't have got much washing done ?.

The fact that it came out when withdrawing the front plate definitely indicates it wasn't tightened properly in the first place, and you have a cr@p installation.

So long as the wires aren't burned back beyond trimming distance this is no big deal. Just buy a decent quality new socket and replace it. Ditto a decent plug for the flex.

It might be worth gradually going round all your other sockets to check terminal tightness as well (switch off at the board first!). There's a bit of craft in getting the torque right - it should be firm, but not torqued down like the wheel nuts on a 44 ton truck! All that does is to strip the threads and/or cut through the copper cable.

Cheers and good luck, Mark.
Thanks Mark...
"Had the brown (Live) wire not been present you wouldn't have got much wasting done ?"
It must have been using the other Brown ?
Not sure where the second lose brown looped to but the as far as I know all the other sockets were working so it was probably still in the terminal until I pulled the faceplate away although it was obviously poorly gripped.
Gary
 
It's quite probably a ring final circuit (32A MCB?), so is intended to be fed power from both cables. On a well loaded circuit, this can cause damage to the fixed wiring, all the way back to the fusebox.
 
Thanks all for great prompt replies.
Only 1 year old good quality (?) BG socket with good quality (?) factory fitted washing machine plug. Permanently plugged in so socket has little use and located in a dry kitchen cupboard adjacent.
Seems to make sense that if it was a poor contact in the terminal there would be more heat damage in that location but as the damage seem to be around the socket and plugs prong, I am guessing it was a poor connection in there.
Got a very nervous homeowner who thinks her house is going to burn down and my ""probably a lose connection"" just isn't good enough.
Arranging for Spark who done the kitchen install to come back and give it the once over to reassure her.
Gary
 
That was my original thinking, lose or missing live overloading neutral?

No, this isn't how electricity works!

The location of the melting / burning clearly shows that this was due to bad contact between the plug pin and socket contact, and unlikely to have been due to loose terminals. Granted the line terminal was apparently loose because the cable pulled out, and a loose terminal can cause a burnout, but in this case it was unrelated.

All contacts rely on tiny (almost invisible) areas of metal actually making contact, so the current density is high and at least some heat is dissipated in the resistance. Less effective contact leads to more heat, which accelerates oxidation of the surface and weakens the spring temper of the socket contact gripping the pin. . This further reduces the contact area and it goes into runaway, leading to a burnout.

Good quality contacts are less likely to suffer from this effect and the socket is the main player rather than the plug. But progressive failure can still be triggered by some random adverse situation like a layer of deposit on the plug pin before installation, and some combinations of plug and socket metal alloys make better contact together than others.

Plugs that are regularly moved have the advantage that any oxide buildup is mechanically scraped off so that fresh bare metal surfaces are exposed. The same is true of the socket contact although heavy use eventually wears out the contact. Again, quality counts and the devil is in the detail, although price is a guide there is no cast-iron guarantee that the most expensive socket will last the longest in a particular application.
 
No, this isn't how electricity works!

The location of the melting / burning clearly shows that this was due to bad contact between the plug pin and socket contact, and unlikely to have been due to loose terminals. Granted the line terminal was apparently loose because the cable pulled out, and a loose terminal can cause a burnout, but in this case it was unrelated.

All contacts rely on tiny (almost invisible) areas of metal actually making contact, so the current density is high and at least some heat is dissipated in the resistance. Less effective contact leads to more heat, which accelerates oxidation of the surface and weakens the spring temper of the socket contact gripping the pin. . This further reduces the contact area and it goes into runaway, leading to a burnout.

Good quality contacts are less likely to suffer from this effect and the socket is the main player rather than the plug. But progressive failure can still be triggered by some random adverse situation like a layer of deposit on the plug pin before installation, and some combinations of plug and socket metal alloys make better contact together than others.

Plugs that are regularly moved have the advantage that any oxide buildup is mechanically scraped off so that fresh bare metal surfaces are exposed. The same is true of the socket contact although heavy use eventually wears out the contact. Again, quality counts and the devil is in the detail, although price is a guide there is no cast-iron guarantee that the most expensive socket will last the longest in a particular application.
Now that, is what I call an answer!
Thank you.
I guess my concern is that I stubbornly refuse to accept that a nearly new good quality plug and socket can fail so badly/dangerously! How many dangerous sockets are out there!?!
Maybe I should sent it to BG for their comment.
Thanks again
 
We can't assume it was 'dangerous' by design or manufacture, because we don't know the actual underlying trigger mechanism for the burnout. Once it starts escalating, any high-resistance fitting can turn into a lump of melted goo, and it has been happening since the first days of electricity. A century ago, when plugs were often made of wood, they would char rather than melt but the result was not very different to what happened to your washing machine plug.
 
I just had that.Tumble dryer stopped.plug and socket too hot to tougch.stank of that burning electrical plastic smell.turned off supply.got plug out.neutral pin had black residue.changed fused,cleaned pin and worked okay in another socket.socket took a very long time to cool down.sparky booked,though tempting to have a look.Q Why didnt the RCD trip?The heat generated indicated that the fault was taking place long enough for the disruption to have been detected.
 
i had similar.tumbler dryer stopped.socket and plug stank and too hot to touch.turned off elec.took out plug cleaned off black residue on neutral pin changed fuse worked okay in another socket.sparky booked though tempting to look inside socket.fake fuses were an issue on domestic appliances a while ago,but old fuse not burnt.As the fault must have been evident for a while to generate such extensive heat which didnt the RCD trip?
 

Reply to Melted Plug and Socket cause in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
619
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hi all I need some advice and thoughts on what caused this plug on a toastie maker to have given me electrical shock when I pulled it out of the...
Replies
6
Views
1K
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
845

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock