Discuss Melted RCD!!! in the UK Electrical Forum area at ElectriciansForums.net

SSE

-
Reaction score
22
My mate asked me to look at his board as a funny smell was coming off it. Looked inside & the neutral going into the RCD was melted & so was the switch. It's a split load dual RCD board. The RCD switches are both rated 64A 30mA. My first thought was that it could have just been a loose neutral but then my second though was maybe the switch wasn't the correct rating. On othis side that the RCD protects he has two rings: one is the downstairs sockets & the other is the kitchen sockets, a 40A shower & a lighting circuit. I know these obviously ain't gonna be drawing their full loads at once but is it still too much?
 
Most likely a poor termination of wiring into the screw clamp of the RCD. I'm sure you'd have noticed most of the other usual suspects such as condensation, insects, debris ingress from drilling above etc. Some pics may confirm if you can upload a couple.
 
Could well be an over load. At one moment in time at lot of loads could have been running simultaneously. It wouldn't take long to over heat the conductors. then the damage just gets worse.
 
Loose neutral is the normal cause of what you describe.
 
Check the resistance between the neutral bar for that RCD and the incomer. Would expect that to show a high reading, pointing to a loose terminal or a faulty RCD.
 
And it's always the neutral that's loose, I'm waiting for the definitive reason why it's always the neutral ;)

it was in the OP that the neutral was melted.
 
Lol they must be the ones that most people forget to tighten.
 
Last edited:
Has all the signs of loose neutral and arcing over a long period of time,seen one recently,80A 30ma main switch,neutral wriggled out easily,so dont expect it was to correct torque,when i had recent assessment the inpsector checked my main switch terminations with his torque driver,spot on,and i dont have one,yet anyway but will get a set as quite handy.
 
And it's always the neutral that's loose, I'm waiting for the definitive reason why it's always the neutral ;)

I have the answer to that one.

It's the same as the Buttered side of toast / bread/ etc, landing on the floor more than the non buttered,, it doesn't.

You remember a neutral being loose, you don't remember the the Live being loose, or even the Earth, on average the same number of times.
 
seems to be a mindset problem with some sparks. tighten the L dog tight, coz it's the important one, but the N is just a return.
 
Sorry guys have no pictures as I just dumped it. I just replaced it like for like. I'll maybe upgrade it to the next size up though just to be sure...thanks for your help.
 
Sorry guys have no pictures as I just dumped it. I just replaced it like for like. I'll maybe upgrade it to the next size up though just to be sure...thanks for your help.

Haha, ...You'll be lucky to see anywhere near 63A for the whole installation, let alone on half an installation!!!
 
The neutral is more prone to burned terminations than the live because the load on the neutral is higher. Non-linear loads such as fluorescent lighting and switch mode power supplies found in computers and other electronic devices cause harmonics in the triplen range which are especially likely to cause high currents or even overloading of the neutral. The effects of harmonics are usually more profound further up the distribution network but they can be an issue at the consumer end as well.

All that aside, as E54 says, I doubt very much that overload was the issue. I'd still bet on a poor termination causing the overheating.
 
The neutral is more prone to burned terminations than the live because the load on the neutral is higher. Non-linear loads such as fluorescent lighting and switch mode power supplies found in computers and other electronic devices cause harmonics in the triplen range which are especially likely to cause high currents or even overloading of the neutral. The effects of harmonics are usually more profound further up the distribution network but they can be an issue at the consumer end as well.

All that aside, as E54 says, I doubt very much that overload was the issue. I'd still bet on a poor termination causing the overheating.
I think it's a domestic single phase installation so the neutral current would be the same.
 
The neutral is more prone to burned terminations than the live because the load on the neutral is higher. Non-linear loads such as fluorescent lighting and switch mode power supplies found in computers and other electronic devices cause harmonics in the triplen range which are especially likely to cause high currents or even overloading of the neutral. The effects of harmonics are usually more profound further up the distribution network but they can be an issue at the consumer end as well.
I concur (well, if I understood!)

I'd still bet on a poor termination causing the overheating.
I'll agree on that as well, never found a (really) loose live or earth, found loads of really loose neutrals.
 

Reply to Melted RCD!!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
253
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
846
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock