Discuss metal capping not needed according to 17th in the Industrial Electricians' Talk area at ElectriciansForums.net

Although we don't use it here I know what capping is for. I just can't work out what metal capping would be for at all though, it just seems pointless.

How dare you suggest such a thing !
Just wait a while and I will rack my brain to think of one!

Mmmmmmmmmmmmmm
Still thinking

Mmmmmm
No,sorry can't think of anything (however trivial the anything may be)
icon11.png



I think you have just sussed out that some of the means of protection that could be afforded gets muddled up by designers who believe myths rather than how to comply,now where's that pot of paint gone
icon10.png
 
So again, what's the point of metal capping, other than to waste money on it?
if you bond it to earth then it becomes an earthed metallic covering as per 522.6.101 (i).

If you don't bond it to earth then it's as much use as a chocolate fireguard, certainly doesn't class as mechanical protection against nail penetration, only protection by sending the fault current down the earth path (and probably tripping the MCB) rather than through the body of the numbnuts who's just banged a nail into the cable, or anyone else who happened to come along at a later date and touch the nail and a radiator or something at the same time.
 
I'm a little surprised to find I'm the first to make that point on page 8 of this thread.

The regulation for mechanical protection is 522.6.101 (iv), the 2 things (mechanical protection and earthed metallic covering) are different classes of protection within the same regulation for protection of cables buried under 50mm from the surface, and can be applied instead of an RCD (unless that's needed for other reasons) and / or when not running cables in safe zones.

(ps that's from the BGB, haven't got the yellow version yet)
 
I'm a little surprised to find I'm the first to make that point on page 8 of this thread.

The regulation for mechanical protection is 522.6.101 (iv), the 2 things (mechanical protection and earthed metallic covering) are different classes of protection within the same regulation for protection of cables buried under 50mm from the surface, and can be applied instead of an RCD (unless that's needed for other reasons) and / or when not running cables in safe zones.

(ps that's from the BGB, haven't got the yellow version yet)

I was thinking of conduit for some reason that's why I've edited.

But I think the metallic covering your talking about is refering to the cable ie s.w.a and not capping.
 
Last edited:
if you bond it to earth then it becomes an earthed metallic covering as per 522.6.101 (i).

If you don't bond it to earth then it's as much use as a chocolate fireguard, certainly doesn't class as mechanical protection against nail penetration, only protection by sending the fault current down the earth path (and probably tripping the MCB) rather than through the body of the numbnuts who's just banged a nail into the cable, or anyone else who happened to come along at a later date and touch the nail and a radiator or something at the same time.
Well that's entirely different as I wasn't aware it could be used like that.

We don't use capping here, its generally 20mm conduit although oval can be used. To the best of my knowledge no wholesalers stock capping, be it plastic or metal.
 
I was thinking of conduit for some reason that's why I've edited.

But I think the metallic covering your talking about is refering to the cable ie s.w.a and not capping.
hmm actually, looks like you're right with that regulation as all the BS's referenced relate to SWA or similar. I'm sure it complies with one of 1,2,3 of that regulation for earthed metal conduit, trunks, ducting etc. Can't see why it wouldn't as long as the capping was equivalent to the CSA of the CPC, but I'm not forking out £100 or so for mutiple BS regulations to see exactly what they say.

It's possible that technically it doesn't comply with those british standards though, but that's how we've used it on occasions where we can't use a 30mA RCD due to the leakage current of inverters. Can't see why there'd be a need to try to have to channel so far into the brick / block to get full conduit in when it only needs protecting from one direction, and isn't relying on mechanical protection.
 

Reply to metal capping not needed according to 17th in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I have a two metre length of 2.5mm T&E running from the loft to a spur under galvanised metal capping (installed during building). Its needs...
Replies
25
Views
2K
Hi everyone, after temporary removing a Sonoff that I've installed years ago to do some painting, I'm unable to get everything back to work. I've...
Replies
4
Views
462
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Hi, I've done some work in a house, I used an existing 10mm cable on a B40 MCB to supply a 2 way consumer unit to control a heat pump and...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock