Reaction score
0
If you are unable to attach a gland to the consumer unit due to having limited space above it (which is where the cables run down) what can you attach or use for the cable entries? Silicone, bush and lock nut?
 
Same methods as with a plastic consumer unit as the IP ratings required for enclosures have not altered. Trunking, boxwork, or blind grommets would all be on my list way above a hole gunked up with silicone sealant.
 
Thanks guys. Wasn't sure on what is/isn't acceptable as the property I'm rewiring will most likely be up for nic inspection. What's confusing me is that metal boards now have to be fitted but plastic can still be used for cable entries. What is the point in that? Or is it just me misunderstanding why the ammendment has been made?
 
Various threads on this subject for some time now. Reg 421.1.201 requires non combustible CU (domestic properties), non ferrous metal is deemed to be a way of achieving that. No mentioned or recommendation of using metal glands, but you can if you want. Only requirement, as it has previously been required, is to maintain the applicable IP ratings. Therefore bespoke glands or blind grommets as has been suggested, trunking, or utilise rear entry for cables. It is only the CU (or similar switch gear assemblies) that now has to be metal, not the method of entry.
 
Last edited:
If you are unable to attach a gland to the consumer unit due to having limited space above it (which is where the cables run down) what can you attach or use for the cable entries? Silicone, bush and lock nut?

I've just been having a similar dilemma and there are actually many different options for maintaining the IP rating when coming in from above SS. See the link to the thread below, but it really just covers what has already been said above although perhaps in a bit more detail. I especially like the video in post 19 which gives you a few options for top entry in order to maintain the IP4X requirement. Saying that, I did exactly as Murdoch has said in post 4 of this thread and just put 2 pieces of 3x2 battens behind, nice bit of plywood for the CU to go on and then brought the cables in through the back therefore negating the need for the IP4X requirement.

I did still use a wiska gland for the tails and main earth though (on the side), which maybe a thought for you if this is a TT (although to be honest I think a 40mm stuffing gland would have sufficed).

http://www.electriciansforums.co.uk...09474-maintaining-ip4x-top-entry-into-cu.html
 
Last edited:

Reply to Metal Consumer Unit - Cable entries? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
775
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
569
Hi can you power a second consumer unit in the garage from our main consumer unit. We have a big armed cable from the main consumer unit into the...
Replies
14
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock