Discuss Metal Supply Cupboard Used As MET in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
3
Hi, first time poster, long time lurker. Guess I'll have to start getting involved...


Just looking for some advice really on something I haven't come across before (I don't usually work on farms).

So I'm working on an installation that is TN-C-S (PME too) and I'm putting in a new TT sub-main to a metal container. Obviously TN-C-S is not preferred on a farm but that's "how its always been" and by the sounds of it / nature of the installation it hasn't caused any issues with animals.

When looking at the incomer I have noticed that the main earth doesn't have a MET and is just bolted into the metal casing; with other earths to sub-mains on the same bolt or bolted in close by. Continuity testing and EFLI is coming back ok suggesting no high impedance connections between these.



I have discussed complete isolation of supply to add in a MET but apparently this isn't an option.

Am I right in thinking this is not acceptable even though tests ok or would this be allowed?
If this is a departure what regulation would you list this under on the EIC?

Thanks

Shaun
 
TL;DR
TN-C-S, Metal incoming supply cupboard used as MET. Departure or not? If so, which regulation?
As a general rule of thumb,

if it is on a farm,

it has been done cheep

it has since been bodged and messed about with by several people who “know about electricity”

is full of dust
rusting away
the covers have been removed and lost many years ago

however to address the point you have raised,
many old and some new distribution boards use their own frame as a point of earthing but normally you would find an earth bar inside that is bolted to the frame for outgoing circuits and any other earth conductors.

if it is good continuity and mechanically sound I would not be concerned.

but my preference when seeing something like that would be to have a nice shiny copper bar with a row of crimped lugs bolted to it.

edit,
p.s. whatever you find will be deemed as safe by the farmer because

“everyone knows that you have to use this piece of wood to operate that thing with the exposed terminals” 😅
 
Last edited:
Sounds like you hit the nail on the head!

Everything rusty and falling apart, but somehow still working. Looks like someone used a random selection of parts they found in the back of their van to bodge it together.

Concerns me a bit that there are NICEIC stickers on some of the work.

Yeah ideally I’d have liked the same, was looking forward to making it all neat really but he wasn’t having any of it ha. Think it’s like a different language to them most of the time anyways.

Thanks, I think I’ll just make a note of the recommendation on the cert and then at least it’s covered.
 

Reply to Metal Supply Cupboard Used As MET in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
752
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
This thread is in relation to the job at the farm I am thinking of taking on (3 phase thread). At present the farm is all PME. I believe it needs...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock