Everything has an IP rating. Are you asking if a water-resistant consumer unit to IP65 is necessary? then I would say no. A meter cabinet provides a reasonable degree of protection. The service head and the meter are not in any way waterproof!
 
Are we talking about a meter cabinet that is embedded into a wall, designed for that purpose?

Ive seen normal consumer units fitted outside in nothing more than what can only be described as a wooden box.
 
In the UK, the DNOs do not permit any equipment other than their own to be fitted in their meter cabinet, although as long as you don't ask, and you position your CU well clear of anywhere you may think that they might fix equipment in the future, then you'll probably get away with it.
The DNO equipment is IP20, but I'd recommend !P55 minimum for anything you may fit
 
In the UK, the DNOs do not permit any equipment other than their own to be fitted in their meter cabinet, although as long as you don't ask, and you position your CU well clear of anywhere you may think that they might fix equipment in the future, then you'll probably get away with it.
The DNO equipment is IP20, but I'd recommend !P55 minimum for anything you may fit
Yes, I am aware of that but thank you for pointing it out.
However, this is a second empty cabinet for the customers use with tails for the garden csu through to the DNO meter cabinet.
 
Metal?????
It will not be inside the premises so a “fire resistant” CU is not necessary.
That was my initial thought and raised that point on here.
I had the following advice :

"It is within the boundary of the dwelling so would need to be compliant."

With the reason for being metal or non combustible obviously being the fire risk, if the meter cabinet is breaching the cavity, is that not a fire risk to the property ? ?
 
you need to weigh up the pros and cons. metal rusts, plastic is not non-combistible.
 

Reply to meter cabinet consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K
Client needs an SPD fitting but no room in c/u or adjacent. Best bet looks like a parallel connection into the tail blocks in the meter cabinet...
Replies
3
Views
277
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
739
I would like to hide the cable to an EV charger. The consumer unit, meter cabinet and charger would all be on the same wall. About 5 metres from...
Replies
19
Views
2K
Hi. Can a horizontal 200A consumer unit be fitted vertically, or is there a vertical configuration? I have a 350mm wide space...thanks.
Replies
19
Views
817

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock