Hi Guys

Just some advice required. I understand meter tails ideally at 3m from meter but is it possible to have meter tails 10-15m from the meter?

Came across a job where there's no real option but to have the consumer unit 10-15m from meter cut out.

If it is possible is additional protection required at meter?

Thanks
 
The usual approach to satisfy everyone is to put the tails cable in as protected (typically using 3 core 25mm SWA, or usual singles in trunking) and feed it from a switched-fuse.

That way you can isolate the long cables as part of the "installation", and the fuse is under your control and (hopefully) chosen to be adequate for 5s disconnection for the end-of-tails Zs value.
 
I have a same problem where tails are in a cavity but customer needs consumer moving up the wall where I can not put in swa cable has space in the DNO cabinit where most metel fuse spurs are to big to go in.
 
It is one of those things that technically the DNO fuse might be enough (depending on Zs) for fault & overload protection so only an isolation switch is needed, but you ought to get the DNO's agreement on that. Hmmm...
 
The usual approach to satisfy everyone is to put the tails cable in as protected (typically using 3 core 25mm SWA, or usual singles in trunking) and feed it from a switched-fuse.

That way you can isolate the long cables as part of the "installation", and the fuse is under your control and (hopefully) chosen to be adequate for 5s disconnection for the end-of-tails Zs value.
Would the switched fuse be local to the meter or 10-15m away local to the consumer unit? Thanks for your reply
 

Reply to Meter tails over 3m in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
418
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
459
Hi, I was hoping someone with a little more insight might be able to shed some light on a potential issue I have, as I can't seem to find another...
Replies
75
Views
7K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock