Discuss micc on rcbo in the UK Electrical Forum area at ElectriciansForums.net

need far more information. Have you insulation resistance tested to the electrical main earth or to the earth of the micc? What does the cable feed? Could there be a crossed neutral? Is the RCBO faulty (disconnection times met and ramp test)
 
to day I have changed a metal cu. micc cable on to rcbo will not set. I then exchange to mcb holds. this existing circuit
What have you changed it from? RCBO detects earth leakage MCB detects Overcurrent, so swapping from RCBO to mcb tells you what exactly, not rocket science is it?
 
Does it need rcd protection, if the circuit is MICC throughout it probably doesn't need it.
 
So the RCBO trips, yet the MCB holds and the IR N-E is 999 - so maybe change the RCBO?

Were the lights "on" with the laps removed when you did your IR?
 
yes pete999 tested line to earth >999 neutral to earth >999
When you swapped from RCBE to MCB is there a chance you could take an earth leakage reading, that may throw some light on the problem, as the problem is pointing to a leakage fault somewhere.
 
IR seems good so cable probably sound. If the total circuit length is great, capacitive leakage can be significant. Use a leakage clamp to measure differential current of L & N, not CPC current and report your findings, also the results for a ramp test of the RCBO.
 
I am asking if the neutral core is connected to the RCBO and not to the neutral bar, as if you have been swapping back and forth MCB to RCBO this could get missed.
If the light fittings are class II then there cannot be an earth fault there so there must be something else causing the problem.
 
This thread made me chuckle. What's been said in it could have been said in 3 posts if the OP had put all the information in to begin with.

OP, does your internet provider charge you extra for using prepositions and the like in sentences? Or where you just replying while there was water on the boil?
 
I am asking if the neutral core is connected to the RCBO and not to the neutral bar, as if you have been swapping back and forth MCB to RCBO this could get missed.
If the light fittings are class II then there cannot be an earth fault there so there must be something else causing the problem.

That is my thought as well especially if all the ir tests come back fine. I didn't mention it because he/she has ignored all my questions.
 
Don't know if this has been asked and I can't be bothered to look back, what voltage was the IR test done at?
 
with the ciircuit connected to MCB, get an earth leakage clamp meter on the job. IR test can sometimes be inconclusive.
 
Used MICC in Council new build flats in the 60s (1960s for the comedians out there)

Yep, the old council spec was mostly either steel conduit or micc both for the flats and communal areas on the local authority where I used to work.

Nowadays its thrown in, cheap and work that a bloke pulled off the street could put his hand to in a day. :(
 
when back to day to look at the job.on to test the micc the reading went mental on IR
looked at the bathroom enclosed light the bowl was full of water & the base
the only thing was missing a gold fish . found out the flat above had a leek
went to the flat below
 
yes pete999 tested line to earth >999 neutral to earth >999

when back to day to look at the job.on to test the micc the reading went mental on IR
looked at the bathroom enclosed light the bowl was full of water & the base
the only thing was missing a gold fish . found out the flat above had a leek
went to the flat below

Now I'm really confused!
 

Reply to micc on rcbo in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've just been fettling some 50 year old 2L2.5 pyro (MICC) to relocate a plug socket. I probably bent the cable a little more than I should have...
Replies
28
Views
977
2 questions.. 1. Will the mini Starbreaker RCBO's fit in this board? Below is a picture of the board and also the type of RCBO I want to fit in...
Replies
3
Views
350
Hi just wondering if someone can help me. I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips...
Replies
10
Views
490
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
842

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock