Discuss Minimum earth for tncs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Ampo

-
Reaction score
15
Hi all, need some help as I'm having a blank. Replacing a consumer unit on a tncs that currently has a run of 2.5 metre tails
16mm tails and 10mm earth. I don't want to waste money for no reason replacing them if not necessary, I know a lot of people would fit 25mm and 16mm earth but the supply is a 60a carrier soni cant see a problem. The issue in having is whether the 10mm earth is ok? I'm looking at table 54.7 and to be honest I'm getting confused with it. Looks to me like its saying it can be less than 16mm but should surely give a size?
 
perfectlyOK. the main earth must be equal,or greater than 50% of the N tail, so 16mm with 1mm is fine, lomuited by ther supply fuse. in this case 60A.
 
Using Table 54.7, up to and including 16mm will require a conductor of the same csa as that of the line conductor. Alternatively you can use the adiabatic equation in 543.1.3
 
It's a bit of an unknown actually, Main protective bonding dictates in table 54.8 that a 10mm^2 conductor is OK for a PEN/CNE up to 35mm^2; however table 54.7 dictates the use of the same size protective conductor up to 16mm^2 (unless you use the adiabatic equation).

This contradiction in the standard leads to on-site guide etc sticking with 16mm^2 minimum to make sure!


BTW the concept of 50% CSA is only: "except where PME apply.."
 
My read of it- happy to hear if I’ve misunderstood :)

If selected - Table 54.7 says to use 16mm

If calculated from Adiabatic Eqn 543.1.3 then because it’s also TNCS/PME then 544.1.1 refers us to Table 54.8 which says it can’t be less than 10mm.

So if the equation says 10mm is ok, then I think it’s ok.
 
It's a bit of an unknown actually, Main protective bonding dictates in table 54.8 that a 10mm^2 conductor is OK for a PEN/CNE up to 35mm^2; however table 54.7 dictates the use of the same size protective conductor up to 16mm^2 (unless you use the adiabatic equation).

This contradiction in the standard leads to on-site guide etc sticking with 16mm^2 minimum to make sure!


BTW the concept of 50% CSA is only: "except where PME apply.."
i stand corrected. get your whip out. :p
 
Table 54.7 is so you do not need to apply any calculations for your protective conductor size. As the earthing arrangement is TNCS, then table 54.8 should be applied for the protective bonding conductor CSA in relation to the PEN conductor (absolutely nothing to do with the Neutral tails csa).
as your existing earthing conductor is 10mm then this will most likely be adequate for the size required as an earthing conductor (adiabatic equation) and meets the size required as a bonding conductor
 
i stand corrected. get your whip out. :p

The 10mmsq bonding conductor is an Electricity supply requirement AKA DNO. The 16mmsq Earthing lead is a DNO requirement. It all started to go wrong years ago when the picture guide book, currently blue decided to flatter itself and give the impression it dictated distribution matters. in fact these matters are "out of scope" of the guide book and any issues should be referred to the local DNO.

Regards, UKPN⚡
 
The 10mmsq bonding conductor is an Electricity supply requirement AKA DNO. The 16mmsq Earthing lead is a DNO requirement. It all started to go wrong years ago when the picture guide book, currently blue decided to flatter itself and give the impression it dictated distribution matters. in fact these matters are "out of scope" of the guide book and any issues should be referred to the local DNO.

Regards, UKPN⚡
“Earthing lead” is that an official DNO term is it?

You are quite right tho, despite table 54.8 the local DNO should confirm their minimum requirements for the csa of the bonding conductors for TNCS arrangements , shame that they are never forthcoming.
 
Last edited:
“Earthing lead” is that an official DNO term is it?

You are quite right tho, despite table 54.8 the local DNO should confirm their minimum requirements for the csa of the bonding conductors for TNCS arrangements , shame that they are never forthcoming.
Don't seem to like maintaining thier provided earth facilities either, it's almost as if they were a law unto themselves....oh wait
 
“Earthing lead” is that an official DNO term is it?

You are quite right tho, despite table 54.8 the local DNO should confirm their minimum requirements for the csa of the bonding conductors for TNCS arrangements , shame that they are never forthcoming.

"never forthcoming" dont know what means, the DNO will always be avail for advice for distribution matters.

But what would I know?
 
"never forthcoming" dont know what means, the DNO will always be avail for advice for distribution matters.

But what would I know?
If experiences like mine are anything to go by, the person on the other end of the phone knows bugger all. Give them an address, an MPAN and ask to know about the connection, earthing arrNgment, supply characteristics etc and you're met with bloody silence, like you're just spoken to them in Klingon
 

Reply to Minimum earth for tncs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
3K
Hi all, just looking for guidance on how you would code a 2.5mm main earthing conductor on a property with 10mm line conductor. Basically on a...
Replies
2
Views
2K
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K
So me and a colleague were having a discussion about using 25mm 3 core swa as a live, neutral, earth and a Bonding conductor when relocating the...
Replies
11
Views
3K
I realise this overlaps with the Earth Rod install post a little, but I am attempting to plan part one of an upgrade. Currently I am mostly...
Replies
24
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock