Hi
I recently visited a property the was experiencing tripping of an Mcb when turning on a 3 kw hand wash appliance in a down stairs loo.
All earth cables present and correct, old wired board but with plug in MCB's No Rcd protection.
Some Numpty had wired the hand wash to the 6 amp alarm and bell circuit with 1mm 3 core cable.
So the MCB was doing its Job.

So i ran 2.5 cable from hand wash unit back to the board to a little used 16amp MCb.
Problem solved. All tests fine and Zs 0.26.

So Minor works certificate ? Installation Certificate? and is it Notifiable?

Any response is greatly appreciated, Thanks.
 
I read to understand that you connected the new cable into an existing circuit at the distribution board? Also does the room contain a bath or shower?
 
Happy to be proved wrong, on face value this seems pretty straight forward to me - it’s notifiable.

Different cable size selected.


It may raise the question whether it should have been notified prior to installation.
 
I wouldn't class this as a major alteration to an existing circuit. Op has wired the appliance in 2.5mm cable into an existing 16A circuit which is likely wired in existing 2.5mm cable - minor works for me and sod notification
 
Very triggers broom replacing the cable and we're.in the db it goes to.
But just a spur off a existing circuit

Who the he'll installed this dryer in the first place, it could of never worked.
 
I'd notify this, in my opinion it's a new circuit.
Not saying that's the definitive answer, just that for the sake of 5 minutes on a computer and a couple of quid I would.
If you had done exactly the same work and there had been a spare way at the cu you would have used that and not thought twice about it.
 
Good debate - I like threads like this. And at least they stay friendly (mostly) these days. Daz
 
It's only an existing MCB though. He's run a new cable. Daz
 
FACT - An existing mcb is NOT a circuit, it is merely a circuit protective device.

FACT - The installation of a new, appropriately rated cable to the handwash unit is clearly a NEW CIRCUIT and is therefore notifiable.


Notification is a total farce BUT trying to convince yourselves that new installations are merely alterations is insulting to the trade.

If a job is notifiable and you you chose not to notify that is your choice ; but surely it is unfair to mislead less experienced forum members with the use of such laughable arguments?
 
Last edited:
FACT - An existing mcb is NOT a circuit, it is merely a circuit protective device.

FACT - The installation of a new, appropriately rated cable to the handwash unit is clearly a NEW CIRCUIT and is therefore notifiable.

But all outgoing wiring connected to a single OCPD is a circuit as defined in bs7671
The installation of a second outgoing cable in to the OCPD of an existing circuit is an alteration to that circuit. However it may be very poor design and not compliant for other reasons
 

Reply to Minor Works? Installation? Notifiable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
259
Hi, A lot about this fault confused me to be honest. So customer complained the doorbell was not working as intended. By that I mean the chime...
Replies
2
Views
695
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
754
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
11
Views
374
Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
439

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock