Discuss Multiple cooking appliances. in the UK Electrical Forum area at ElectriciansForums.net

You're right, but I've got it now. Your maths are correct, or I make the same mistake :)
The answer is quite different using Table A1 method, as its got 3 lots of 10A, vs only one lot when using Table A2. I think A2 is the one to use for this, just going by its name (?).
So table A2 by using the total loads, I'm getting 41.5 A after diversity ?
 
Hmmm you could be on to something here, another little known fact is that Tel and Pete are actually twins. :D
not treue. pete is 4 months older than me. that,s 18 weeks to correct the minor defects and create perfection.
 
You're right, but I've got it now. Your maths are correct, or I make the same mistake :)
The answer is quite different using Table A1 method, as its got 3 lots of 10A, vs only one lot when using Table A2. I think A2 is the one to use for this, just going by its name (?).

According to the introduction on Appendix A, Table A1 is used to calculate the current demand for a final circuit, making an allowance for diversity. Table A2 is used for calculating the current demand of an installation consisting of a number of final circuits, also making an allowance for diversity.

The 'definition' used in both (for cooking appliances) is the same (IMO), although they are written differently.

Appendix H, and H4 advises the use of Table A1 for cooker circuits in household premises. It states that a 30 or 32 A circuit is usually appropriate for household or similar cookers of a rating up to 15kW. It also advises about the connection of two or more appliances on one circuit.

Mind you, these diversity tables were composed 'hundreds' of years ago, before induction hobs, steam ovens etc were introduced. Down to the designer. :)
 
steam ovens? are we now regressing back to the age of steam, when things were designed and engineered to perform, regardless of accountants going for cheapest option,, broken within weeks instead of decades?
 
No not steam engines, steam ovens bit like this;

Hot tub.png
 
According to the introduction on Appendix A, Table A1 is used to calculate the current demand for a final circuit, making an allowance for diversity. Table A2 is used for calculating the current demand of an installation consisting of a number of final circuits, also making an allowance for diversity ...

Re reading the docs, I see what you mean and I'm seeing the wisdom. Table A1 title has "points of utilisation or current using equipment" and in this case there are 3 of them, so apply it 3 times :)

Learning everyday, cheers !
 
Re reading the docs, I see what you mean and I'm seeing the wisdom. Table A1 title has "points of utilisation or current using equipment" and in this case there are 3 of them, so apply it 3 times :)

Learning everyday, cheers !
So in your opinion Wilko would you go by 3 different applications of the 10A +30% calc and cover all (15kW) on one 50A control switch or seperate radial say for one appliance and seperate isolator of course ?
 
I think if you have one existing 32A radial, I'd be inclined to drag in another. If you have a butchers at H4 OSG (described by some, as a storybook with pictures), it makes reference to isolation, and refers to reg 536.2, which I can't make sense of, but think says refer to manufacturer?
 
Isn't the problem that you've only got 6mm and a 32A mcb? Now I've smelt the cooking I def would not add this new hob to that circuit, a change from what I implied at 6:30 this morning ...(darn, too late to edit?). If circuit was at least 40A then it's a maybe but we are back to actual useage vs OSG advice. A 2nd 6mm and it can be Christmas every day :)
 
I think if you have one existing 32A radial, I'd be inclined to drag in another. If you have a butchers at H4 OSG (described by some, as a storybook with pictures), it makes reference to isolation, and refers to reg 536.2, which I can't make sense of, but think says refer to manufacturer?
Yes mate, I did read that and the reg which is another quite flouncy sentence :D and in my mind is taken as add an isolation switch to switch the appliances conveniently rather than one switch to shut off 3 different appliances for instance. Either way thanks for input from all ;) I'm nearly off to the airport as Mallorca soon !
 
At least take the OSG with you for lying by the pool reading material - you'll be clued up by the time you return!
Happy holiday!
Yes mate, I did read that and the reg which is another quite flouncy sentence :D and in my mind is taken as add an isolation switch to switch the appliances conveniently rather than one switch to shut off 3 different appliances for instance. Either way thanks for input from all ;) I'm nearly off to the airport as Mallorca soon !
 

Reply to Multiple cooking appliances. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
Hi all, I'm getting a 32a induction hob and a 13a oven installed as part of a kitchen refurb. The existing cooker circuit is 6mm protected by a...
Replies
7
Views
2K
Hello all, I'm in the process of having my kitchen refurbished and I'm looking for advice on my current setup as I have been told that I will...
Replies
15
Views
3K
Evening all, I'm upgrading my kitchen electrics replacing the current gas hob for an induction hob. The oven was previously plugged into the...
Replies
6
Views
2K
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock