Search the forum,

Discuss Neutral bar in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi
What’s the principle .
with a neutral not connected to the neutral bar will be 230v basically a line.
But when neutral is connected to neutral bar there is 0v.
Neutral and earth are connected further on with the same potential but I still don’t understand how the neutral bar and even the earth bar isn’t at 230v ?
 
Hi
What’s the principle .
with a neutral not connected to the neutral bar will be 230v basically a line.
230V between N and what?

What makes you think there will be a potential difference of 230V between N and whatever-it-is?

But when neutral is connected to neutral bar there is 0v.
0V between N and what?


Neutral and earth are connected further on
Downstream of the cutout they'd better not be.


I still don’t understand how the neutral bar and even the earth bar isn’t at 230v ?
230V between them and what?


Assuming (as seems reasonable), you're talking about the regular 230/400V public supply in the UK, the star point of the supply transformer is N and is tied to earth.

1618353757362.png


Each phase is 230V wrt that.


Not sure what it is you're asking/don't understand....
 
I think he's saying that as a N conductor has potential of 230v if loose, then you connect it to a N bar, why isn't the N bar then at a 230v potential. And on TNCS systems as he correctly says the Earth is connected to the Neutral so in turn why isn't that at 230v potential.

The simple answer is that as per the diagrams above the N in the supply is connected to the mass of real earth so is held at a fixed potential of 0v.

For current to flow we need a potential difference; with a completed circuit we have a potential difference peaking at 230v to 0v half the time, and -230v to 0v the other half of the time.
When all connected normally current can flow, and the amount that flows depends on the resistance of the circuit load.
With N disconnected there is no completed circuit between two potential difference points, the N end of the circuit is "floating" so remains at 230v.
 
I think he's saying that as a N conductor has potential of 230v if loose,
Sorry - when you say "loose", what do you mean?

And 230V wrt what?


then you connect it to a N bar,
Before you do that, what makes it a N conductor?


why isn't the N bar then at a 230v potential.
Why isn't it at 230V to what?

Why is is a "N bar"? What makes it so? What properties does it have?

And on TNCS systems as he correctly says the Earth is connected to the Neutral so in turn why isn't that at 230v potential.
Why isn't that at 230v potential to what?


The simple answer is that as per the diagrams above the N in the supply is connected to the mass of real earth so is held at a fixed potential of 0v.
Held at a fixed potential of 0v to what?

For current to flow we need a potential difference; with a completed circuit we have a potential difference peaking at 230v to 0v half the time, and -230v to 0v the other half of the time.
325V, actually.


With N disconnected there is no completed circuit between two potential difference points, the N end of the circuit is "floating" so remains at 230v.
Disconnected from what?

Why are you calling this disconnected thing neutral?

It remains at 230V to what?
 
Talking 'return'. A return cable has to be connected to 'Neutral' to become a neutral. If not, the circuit's incomplete. Testing whilst disconnected, it's in series with the live supply.
 
Ah - this is the trouble. It's not being picky - understanding how circuits are completed, and how a potential difference has to be between two points which are in the same frame of reference, and what that PD is, and when, and why, is fundamental and crucial.

If you disconnected a circuit conductor from an MCB, would you still call it the line conductor? What would you call it if you connected it to the + terminal of a 12V car battery which wasn't connected to anything else?
 
@Soi disant I know what you are getting at and agree the terminology is not exactly spot on but I think we’re going down rabbit holes a bit and we don’t want to scare the OP away.
 
@Soi disant the OP is a trainee and you firing short sharp responses back to other people's posts is not going to help anyone.

Sorry - didn't mean it aggressively or anything - just trying to break it down into basic fragments, and to get people to think about them.....

I strongly suspect that the OP actually understands more than he thinks he does, or at least would understand more, if he thought about the things he already knows.
 
@OP.basically, in normal service the 230V is dropped across the load/s. if you disconnect the neutral from the supply side, there is no current flow and hence no volt drop, sot the N is at a 230V potential. ohms law V=IR, where I =0, then VD =0.
 
if you disconnect the neutral from the supply side, there is no current flow and hence no volt drop, sot the N is at a 230V potential.
No, it isn't. The supply neutral is still at a nominal 0V to earth, and the supply line is still at a nominal 230V to N & E.

What you have disconnected is no longer the neutral. It inherits its status as neutral by being connected to the neutral point in its frame of reference, i.e. the supply neutral. If you disconnect it from that it loses that status.

Most of the time that distinction doesn't matter, but it absolutely does when trying to understand that voltages are not singular, isolated things but are a difference in electrical potential between two points.
 
Last edited by a moderator:
No, it isn't. The supply neutral is still at a nominal 0V to earth, and the supply line is still at a nominal 230V to N & E.

What you have disconnected is no longer the neutral. It inherits its status as neutral by being connected to the neutral point in its frame of reference, i.e. the supply neutral. If you disconnect it from that it loses that status.

Most of the time that distinction doesn't matter, but it absolutely does when trying to understand that voltages are not singular, isolated things but are a difference in electrical potential between two points.
that's what i said.it's no longer a neutral as it's not referenced to 0v any more. you seem to have a penchant for twisting posts to suit your own ideas.
 
Another thing which is not going to help anyone is loose, sloppy, terminology.
I think you are taking this a tad far!
It would appear from your logic that you'd like me to write "Broken line conductor which used to be a neutral conductor before it was broken and is insulated using black pvc according to pre-harmonised standards" on reports. I think I'd prefer to be loose and sloppy. You should try it too. The liberation feels amazing!
In fact I've just said "Neutral" to another sparky even though it isn't connected yet. Astoundingly they understood me. It felt great!
 
that's what i said.it's no longer a neutral as it's not referenced to 0v any more.
Well, actually no, you didn't, you said this (with my emphasis):

if you disconnect the neutral from the supply side, there is no current flow and hence no volt drop, sot the N is at a 230V potential.
And that's not me twisting things, and again, it's not me trying to start a fight. It's me trying, and failing, to get across what I think is a very important fundamental point.

If you had a 9V battery, with a bulb connected across it, and you disconnected, at the battery, the wire attached to the -ve terminal, it would no longer be a -ve wire. Were you to connect a voltmeter to it to measure what voltage it was at wrt battery - you would find that it was at +9V, and you would not be able to measure -9V between it and the battery +. It wouldn't be a -ve wire.

Of course this distinction doesn't matter most of the time when you're talking about the wires from the bulb holder, ditto the N conductor as per above, which is what I'd already said in #15, so in no way am I arguing with
In fact I've just said "Neutral" to another sparky even though it isn't connected yet. Astoundingly they understood me. It felt great!

It's just that when someone is trying to get to grips with what is meant by "+9V", or "230V AC", about what potential differences exist between what points in a circuit, and when, and why, and why current flows, or does not flow, I think it is important to focus very precisely on what something actually is.

I'm sorry that I'm failing so badly to explain that people think I'm really trying to make trouble.
 
I'm sorry that I'm failing so badly to explain that people think I'm really trying to make trouble.
I do think there has been some misunderstanding of intent. Trust me you have explained your point!
Sorry I was flippant. I just didn't want the poor chap to go off and become a plumber while we were arguing how best to describe a disconnected line conductor (and in fact his original post suggests he already understood this as a line conductor!)

(I also meant to say thank you for reminding me of the 325v peak waveform - it's been a long while since I did the x 1.414 maths for a WYE configuration)
 
So, with all this, 'neutral or not' talk, how do we test the RFC continuity of the 'neutral' (r n) on the circuit............. if it isn't connected to anything?
We've got to presume, sometimes.


IMG_1300.jpg


It's like explaining a N fault (disconnected)

'There's a disconnected cable fault'
' What cable?'
'The blue one'.
'Is that the neutral?'
'No'.
'Well which one is it, then?'
'The one that's disconnected'.
Oh, fair enough, which one have you reconnected to clear the fault?
The neutral, of course'.


There's a hole in my bucket, dear Liza, dear Liza.
 
So, with all this, 'neutral or not' talk, how do we test the RFC continuity of the 'neutral' (r n) on the circuit............. if it isn't connected to anything?
We've got to presume, sometimes.


View attachment 84642

It's like explaining a N fault (disconnected)

'There's a disconnected cable fault'
' What cable?'
'The blue one'.
'Is that the neutral?'
'No'.
'Well which one is it, then?'
'The one that's disconnected'.
Oh, fair enough, which one have you reconnected to clear the fault?
The neutral, of course'.


There's a hole in my bucket, dear Liza, dear Liza.
Nice. Good argument there.

We're talking about a cable intended to be neutral. Only a severely afflicted pedant would attempt to argue otherwise.?
 
I think it was Lucian who pointed out a couple of months ago that the fact the N conductor is connected to earth, at some point, is what defines it as "neutral" compared to the line conductor(s).

The common earthing systems such as TN-S, TN-C-S and TT all revolve around how you connect to earth relative to the neutral conductor (separate, common PEN, or via the true Earth). Even IT systems usually have some high impedance means of referencing one conductor to the Earth's potential, for insulation monitoring if nothing else.

Even there, the choice of the Earth as 0V is simply a convention, certainly a reasonable one to justify, but it is still an arbitrary choice of what we mean when we say 0V in an absolute sense, rather than a voltage difference sense.

Mars is a bit for for an "earth rod" to get another opinion on 0V!
 
I would imagine the O.P is sat in a corner quivering, wishing he'd never come on here and asked the question.

This thread needs deleting with the exception of the O.P and let it start again, without all the arguements over when is a Neutral not a Neutral.

It was a relatively simple question requiring a relatively basic answer.
 

Reply to Neutral bar in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
Hi just wondering if someone can help me. I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips...
Replies
10
Views
512
I have breaker box at least 40 yrs old, both conduit and romex enter box, only one neutral bar that all white wires and bare ground wires attach...
Replies
4
Views
767
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
399
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock