Discuss neutral earth fault in the UK Electrical Forum area at ElectriciansForums.net

D

dave1064

During my zs tests on the ring circuit the rcbo trips. The breaker also trips when I take a Zs on the cooker. I have carried an insulation resistance test on the cables and have found a dead short (0.00) Mohm reading on the neutral and earth on the ring circuit. 137 between line and earth and 87 between neutral and line both these readings not great but acceptable.

Why is the rcbo not tripping straight away when energised?

I have changed the rcbo too.
 
During my zs tests on the ring circuit the rcbo trips. The breaker also trips when I take a Zs on the cooker. I have carried an insulation resistance test on the cables and have found a dead short (0.00) Mohm reading on the neutral and earth on the ring circuit. 137 between line and earth and 87 between neutral and line both these readings not great but acceptable.

Why is the rcbo not tripping straight away when energised?

I have changed the rcbo too.

These readings do not make sense, if you have short circuit N-E you would be getting the same reading between L and E as you get between L and N
 
It sounds like you may still have equipment left connected to the circuits under test.

What tester are you using? Some testers will trip an MCB/RCBO under test, and if this is the case you might have to calculate your Zs manually if you have a measured R1+R2 value
 
During my zs tests on the ring circuit the rcbo trips. The breaker also trips when I take a Zs on the cooker. I have carried an insulation resistance test on the cables and have found a dead short (0.00) Mohm reading on the neutral and earth on the ring circuit. 137 between line and earth and 87 between neutral and line both these readings not great but acceptable.

Why is the rcbo not tripping straight away when energised?

I have changed the rcbo too.
There's a fault I suspect, however before getting into that did you do the ZS test with the non trip function lol
 
The rcbos will trip because you are sending current to earth, the very thing they are there to stop.
Dead short n-e, yes of course, they are the same thing.
Rcbo does not trip when energised because it is seeing no fault (or you have killed it with your megger).
Maybe time to say who you are so we can understand why you are having problems with such basic stuff.IE are you a young tradesman, apprentice, Electrical Trainee, mate?

Boydy
 
Maybe time to say who you are so we can understand why you are having problems with such basic stuff.IE are you a young tradesman, apprentice, Electrical Trainee, mate?

Boydy

from an earlier thread;

Im a 4th year apprentice due to sit my trade test in 2 weeks. So been studying etc. And the question was asked why it is 0.8. Just wondered how they came up with 0.8 ohms
 
4th year apprentice, a rare breed these days, respect.
Can you please answer the question in post 5, it is very relevant.

Boydy
 

Reply to neutral earth fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
513
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock