Hi, is it a requirement to run an earth wire to outside light(although its double insulated) or is it probably just best practice ? I was replacing my son,s existing outside light on a new build house with a pir security light but found there was no earth to his existing light. Thanks
 
Hi, is it a requirement to run an earth wire to outside light(although its double insulated) or is it probably just best practice ? I was replacing my son,s existing outside light on a new build house with a pir security light but found there was no earth to his existing light. Thanks
All electrical points require a cpc (earth wire) whether used or not
 
Either I'm going blind or it's not in the book that every circuit shall have a CPC?

Sanity check please, 543 onwards.
 
Have a closer look, guess the new build sparky has snipped off the annoying earth wire; it'll be hidden inside the outer sheathing.
 
you might want to check all the lighting points for a cpc. Switches and lights.
I would think a new build domestic property would be wired in grey twin and earth.... and the earth is there, just cut off.
It could be a pain if there’s not enough spare cable to pull
 
Every point in the wiring (not just every circuit) must have a cpc terminated. So obviously a cpc is required at a luminaire, whether inside or outside.
But where is it written? I'm not being pedantic, I can't find it in the book.
 
06F8DAA9-E33A-4BBA-8A17-11E5F1AAB986.jpeg
 
While we’re on he subject then, if say a klix box has a cpc to it, I am ok to plug 2c off that to class 2 fittings?
I would personally say that the cable from the klix box should be at least a 3 core (containing a cpc) as it is not the same as a lamp holder given as an exception in the regulation unless your primary means of protection is the protective measure double Or reinforced insulation which is not permitted in a domestic installation.
 
Noting one should never say never, I can't believe a new build with no CPC at the light fitting. It's very likely there but has been cut back at the end of the grey sheath rather than spend 10 seconds terminating it properly.
 
If the light is double insulated then ADS is not applicable so the earth to the point is a non-starter.

A double insulated piece of electrical equipment does not need an earth run to it.
 
If the luminare is supplied by way of a lighting coupler such as a ceiling rose I see no point in providing an earth to the fitting. If it is connected directly then the presence of a cpc is likely to be present in the cable. If at some point the fitting is replaced with a unit which requires an earth then the means of providing this should be readily accessible so if a ceiling rose is employed it should not be inaccessible.
 
Essex, what happens in my son,s case, when he is changing the existing light fitting for a different one. Is it just tough luck, you will now need to run in your own earth now ?
Seems a bit shabby for a new build.
 
Essex, what happens in my son,s case, when he is changing the existing light fitting for a different one. Is it just tough luck, you will now need to run in your own earth now ?
Seems a bit shabby for a new build.
If the luminare is supplied by way of a lighting coupler such as a ceiling rose I see no point in providing an earth to the fitting. If it is connected directly then the presence of a cpc is likely to be present in the cable. If at some point the fitting is replaced with a unit which requires an earth then the means of providing this should be readily accessible so if a ceiling rose is employed it should not be inaccessible.
If the luminare is supplied by way of a lighting coupler such as a ceiling rose I see no point in providing an earth to the fitting. If it is connected directly then the presence of a cpc is likely to be present in the cable. If at some point the fitting is replaced with a unit which requires an earth then the means of providing this should be readily accessible so if a ceiling rose is employed it should not be inaccessible.
The luminaire is an outside light mounted on a rendered wall
 
Essex, what happens in my son,s case, when he is changing the existing light fitting for a different one. Is it just tough luck, you will now need to run in your own earth now ?
Seems a bit shabby for a new build.

I agree it is a bit crap and there may be a specific regulation that states all cables shall be terminated correctly somewhere in the regs but someone else may be able to assist there. That is of course if the CPC has just been cut off short - which is likely.
 
I agree it is a bit crap and there may be a specific regulation that states all cables shall be terminated correctly somewhere in the regs but someone else may be able to assist there. That is of course if the CPC has just been cut off short - which is likely.
Yes I will check that next time I,m up at their house. We babysit once a week, they live 55 miles away from uf !
 
In case someone drills a nice hole into the cable in the wall...........

I don't follow. There is no guarantee that someone would hit the CPC and live conductor. The circuit would also still disconnect if the live and neutral was hit.

There are other things in place to prevent electric shock from drilling.
 
I don't follow. There is no guarantee that someone would hit the CPC and live conductor. The circuit would also still disconnect if the live and neutral was hit.

There are other things in place to prevent electric shock from drilling.
And what if they didn't hit the live and neutral just the live and earth.......or in your case just the live because there is no earth........
 
And what if they didn't hit the live and neutral just the live and earth.......or in your case just the live because there is no earth........

To be fair, I experienced a fault, where a previous home owner had nailed a dado rail to a wall, nicking just one strapper in a tw&e. Livened up the whole wall for the next 10 years, depending on which way the landing light was switched.
 
To be fair, I experienced a fault, where a previous home owner had nailed a dado rail to a wall, nicking just one strapper in a tw&e. Livened up the whole wall for the next 10 years, depending on which way the landing light was switched.
Nice.......but I bet he had an earth.....seems that Essex is quite prepared to run a cable to an external light without one
 
Nice.......but I bet he had an earth.....seems that Essex is quite prepared to run a cable to an external light without one

I don't think so; I think he is trying to cite what the regulations state, in which he appears to be correct.

However, this is not helping the OP.
 
Why would a new installation be installed in such a way, so that the potential unknown owner would have to install Class 2 luminaires?

To coin previous catch phrases, although not impossible, just very unlikely.

I am not doubting there stupidity, just debating whether it is actually against BS 7671.
 
Nice.......but I bet he had an earth.....seems that Essex is quite prepared to run a cable to an external light without one

Whether it had an earth or not is irrelevant as in the example it counted for nothing.

I would be happy to run a cable to any double insulated electrical equipment with no earth as it is specifically stated that an earth is not required. Would I do it in the ops case - no.
 
I am not doubting there stupidity, just debating whether it is actually against BS 7671.

Ok, but it doesn't help the OP; we all know - unless the particular installer had gone wibble that day - that there will be a cpc at this particular point in question. OP just has to look for it. Now he knows this is the normal accepted way of doing things.
 
I am not doubting there stupidity, just debating whether it is actually against BS 7671.
Hi - if I've understood correctly, you've asked does BS7671 specify a cpc shall be run with a circuit (?). If so, referring to Reg 543.6.1, I think that is a yes in this case.
 

Reply to New build outside light in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Metal building with living quarters the panel is on the outside and about 20 feet away from new build that will be 2x6 what type of shielded wire...
Replies
3
Views
572
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
496
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
545
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
561
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock