134.1.1 & 510.3 & 526.203 - Bet Wago haven't approved the product for such useAgree …trunking is an enclosure.
526.3.vi - Not MF in the current state
Discuss New fuseboard fitted badly in the UK Electrical Forum area at ElectriciansForums.net
134.1.1 & 510.3 & 526.203 - Bet Wago haven't approved the product for such useAgree …trunking is an enclosure.
Trunking can generally be accessed by just pulling the lid off, is there anything in the UK Regs, as in France, that says to be in an enclosure only accessible by the use of a tool?Agree …trunking is an enclosure.
That is my understanding, so a length of ordinary plastic trunking is not suitable for joining cables, unless the joiners themselves are enclosed inside the trunking.by something that needs a tool to open it.Trunking can generally be accessed by just pulling the lid off, is there anything in the UK Regs, as in France, that says to be in an enclosure only accessible by the use of a tool?
I WOULD EXPECT THE SAME .Trunking can generally be accessed by just pulling the lid off, is there anything in the UK Regs, as in France, that says to be in an enclosure only accessible by the use of a tool?
No such reg526.203
A ceiling rose cover, for example, can be also be removed without the use of a tool. Thus revealing live connections. I would be ok with a properly made joint in PVC trunking. In fact the lid is often hard to remove.Trunking can generally be accessed by just pulling the lid off, is there anything in the UK Regs, as in France, that says to be in an enclosure only accessible by the use of a tool?