Discuss New metal roof on existing concrete garage in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hello all, I need some advice please.

We have a detached concrete sectional garage that is one of a semi detached pair with our neighbour. The garage has power (via SWA off a fused spur within the house with earthing provided back to the TN-C-S supply). One double socket and a light via a 3amp spur. All has been tested and found to be fine. The garage has a metal up and over door that was not deemed to be an extraneous conductive part when the power was installed or when recently examined and tested as part of a periodic inspection.

The roof is currently cement board (corrugated with white asbestos) and the neighbour has damaged theirs such that it needs replacement.

The roof spans both garages so his insurer intends to replace both with powder coated profiled metal. A new non asbestos roof is a nice present.

The insurer plans no changes to the power provision as they state that the metal roof isn't in contact with the grounŷd and so is not an extraneous conductive part.

Given we currently have a fully happy periodic inspection in place for the whole house and garage I need to make sure they are correct and that we don't need the new roof bonding (10mm cable back to the meter point would be one heck of a task (it's on the other outside wall of the house and this is a mid terrace) so a TT spike solution would probably be needed).

Is a metal roof that a) connects to next door and b) isn't in contact with the ground an extraneous conductive part? If so, was the garage door already one? The guy who does our electrical work has just started his 3 week holiday in Florida, hence asking your learned selves here so we don't end up with a problem after the insurers' contractor leaves.

Thanks in advance....
 
If garage door is outside must be connected to the Equipotential Ground and all metallic hand contact see the Law of Electrical Ground and Schematics Diagram for Earth Ground. Prevent Atmospheric Electrostatic also.

The Forum is based around the British Standards BS7671 and advice given should fall within these standards unless otherwise specified, I assume your own regulations differ to ours so please if giving advice make it clear which regulations you are citing your information. We of course welcome members from across the globe but heed caution when offering advice that you are not doing so in contradiction of our British Standards unless the thread or post has specifically asked for advice regarding other reg's.
 
Just don't mention the Scottish...
 
The Forum is based around the British Standards BS7671 and advice given should fall within these standards unless otherwise specified, I assume your own regulations differ to ours so please if giving advice make it clear which regulations you are citing your information. We of course welcome members from across the globe but heed caution when offering advice that you are not doing so in contradiction of our British Standards unless the thread or post has specifically asked for advice regarding other reg's.
maybe romania have just got the 15th.
 
The salient points here are that one; if the insurers state in writing that bonding is not needed then they will be liable for any damage or harm that arises from same
two; the landlord is responsible for the electrical safety of tenants and must satisfy himself this is true.
Perhaps ask the insurers to pay for a certificate to be issued regards the facts stated. After all they are insurers not electricians. With all due respect to opinions offered here, they will not cover you in the event of harm to property or person. For instance there is a greater risk of lightning damage now you have a metal roof.
 
The salient points here are that one; if the insurers state in writing that bonding is not needed then they will be liable for any damage or harm that arises from same
two; the landlord is responsible for the electrical safety of tenants and must satisfy himself this is true.
Perhaps ask the insurers to pay for a certificate to be issued regards the facts stated. After all they are insurers not electricians. With all due respect to opinions offered here, they will not cover you in the event of harm to property or person. For instance there is a greater risk of lightning damage now you have a metal roof.

There's an even greater chance of a lightning strike if it is earthed.
 
The salient points here are that one; if the insurers state in writing that bonding is not needed then they will be liable for any damage or harm that arises from same
two; the landlord is responsible for the electrical safety of tenants and must satisfy himself this is true.
Perhaps ask the insurers to pay for a certificate to be issued regards the facts stated. After all they are insurers not electricians. With all due respect to opinions offered here, they will not cover you in the event of harm to property or person. For instance there is a greater risk of lightning damage now you have a metal roof.
Having a metal roof does not increase the risk of lightning strike it will make no difference what so ever. It may actually protect the building by dissipating it over its large conductive area. Lightning seeks a path of least resistance to earth and an isolated metal roof will not draw its attention, it is more likely to go for the tall tree next to it. Lightning protection draws the charge from the building structure to earth by its lower resistance path, lightning protection and any associated attractors do not necessarily draw the lightning towards them it merely deflects it once it strikes. Main protective bonding to these parts is a recent requirement to stop the lightning being attracted to internal circuit protective conductors which can result in damage.
 
Last edited:

Reply to New metal roof on existing concrete garage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
771
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
889
I have found out that my electricity supply in my external garage is wrongly connected to my neighbours electricity unit in their house and their...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock