Evening all,

Thank you for all your advice recently. I eventually tracked down the a broken cpc in a junction box which was broken where the cable came into the jb not at the terminal. There where also a few loose connections on some old face plates.

Cheers all, just about start my next thread as i need some more advice
 
I'm glad the OP has found and fixed his fault, which luckily doesn't sound like it needed the house torn apart to access.

But I don't agree with this at all:

Best way and clearest way to pinpoint the problem would be to firstly liven up the ring affected only... until you reach the leg that fails to give you 230v between line and cpc

The OP says his 'break' measures 300 ohms. A voltage indicator will see straight through that and continue to show voltage beyond the fault. If, on the other hand, the fault does go open circuit, connecting the indicator beyond it will raise the disconnected section of CPC and any associated metalwork to an elevated voltage, and one is then relying on the test current being limited to avoid creating a shock hazard.

My point is this (and it's a point I've made before) Why use a potentially unreliable live test when the fault has been effectively shown up by a dead test? Why would you not continue tracing with an ohmmeter?
 

Reply to no cpc continuity on ring final, strange readings ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
302
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
506
I read that it is against the regs that a ring final circuit cannot be just a ring with with spurs off it. In short, a ring must have sockets on...
Replies
86
Views
6K
Hello, I’m testing some electric meters. As the circuits have no load on them to prove each ct I’ve plugged a hair dryer to simulate a load and...
Replies
3
Views
472

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock