Discuss NO EARTH FOUND ... can I change my system to pme myself? in the Electricians' Talk area at ElectriciansForums.net

T

thekernal

Think the builder ripped the earth rod out... Whatever happened there's not an earth now. Instead of installing a new one am I allowed to take the neutral from the metre and connect a main earthing conductor in a henley block.
The street does have pme available, I checked. Is it legal though???
 
Was the original earthing scheme TT? I would reinstall a nice new rod and if you have problems getting a decent Ra value then look at converting to TNCS. I'd assume you'd need to contact the DNO or energy resaler with regard to PME'ing the installation.
 
Think the builder ripped the earth rod out... Whatever happened there's not an earth now. Instead of installing a new one am I allowed to take the neutral from the metre and connect a main earthing conductor in a henley block.
The street does have pme available, I checked. Is it legal though???

Gasp!!!!
 
kernal. that's another name for nut. and you will be one if you try that.
 
Think the builder ripped the earth rod out... Whatever happened there's not an earth now. Instead of installing a new one am I allowed to take the neutral from the metre and connect a main earthing conductor in a henley block.
The street does have pme available, I checked. Is it legal though???[/QUOTE]

Your not an experienced qualified electrician are you??

The answer to both your questions is NO!!!
 

Reply to NO EARTH FOUND ... can I change my system to pme myself? in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
834
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
At a house today fitting yet another car charger. Straightforward install apart from fuse holder having a crack in it. Called SSEN who sent an...
Replies
8
Views
4K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock