Discuss No RCD domestic lighting in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
17
Firstly sorry if this has been asked before. Carrying out alot of EICRs because of the new rental laws. Keep coming across boards with just one RCD. Lighting circuits not protected normally I issue a C2 for this and had no problems but one landlord who thinks he knows everything has queried my decision today What would you guys give it C2 or C3
 
Well has the potential to be otherwise why change the regs in the first place
[automerge]1593719072[/automerge]
I issue C2 as that is what I was advised by Stroma when I was with them before I changes that is
 
I don’t have the BBB here, but I’m pretty sure there’s a statement right near the front from the HSE about older installations installed to previous editions not being inherently unsafe just because the regulations have changed to improve safety.

Obviously some things that were allowed were dangerous and hence became banned, but additional protection by RCD is just that, additional protection.
 
So not retrospective take a bathroom with a pendant light or a batten lamp holder clearly not IP rated would you just leave it and say it's fine. An outside socket fitted before RCD were fitted would that be ok. Think I'm just going to stick to my guns on this one. If they dont like my comments they can go else where. When its safety I always ere on the safer side just for the sake of a a few quid
 
Well has the potential to be otherwise why change the regs in the first place
[automerge]1593719072[/automerge]
I issue C2 as that is what I was advised by Stroma when I was with them before I changes that is
What was your opinion before the brains trust at Stroma gave their unconsidered opinion. Any electrical system has the potential for danger.
 
Like I said for the sake of an rcbo or additional rcd in the board for a few quid is it really worth taking unnecessary risks. We wouldn't fit things with out an rcd today would we.
My opinion right or wrong is it could be potentially dangerous
 
Like I said for the sake of an rcbo or additional rcd in the board for a few quid is it really worth taking unnecessary risks. We wouldn't fit things with out an rcd today would we.
My opinion right or wrong is it could be potentially dangerous
That’s why I’d c3 it, make the owner aware...end of the day all it comes down to is the inspectors opinion ?
 

Reply to No RCD domestic lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
589
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
763
Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K
Client has purchased a night flat in Edinburgh. Its perfect for using as a ST rental during the festival as the agents claim £6k a week is the...
Replies
67
Views
6K
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock