Hi all,
I got job which client ask me to replace 20 down lights and install new bathroom extractor fan but DB is not RCD protected.(client dose not want change DB )
can I do my job without changing DB or I must change DB?
Thank you
 
Hi all,
I got job which client ask me to replace 20 down lights and install new bathroom extractor fan but DB is not RCD protected.(client dose not want change DB )
can I do my job without changing DB or I must change DB?
Thank you
If your works will involve alterations(adding lights?) You will require additional protection for the lighting as it’s domestic and for the circuits serving the bathroom location. If it’s like for like replacement items then it could be classed as just maintenance and not an alteration or addition to the existing installation.
 
Last edited:
changing lights, like for like, is no problem. if the fan is a replacement, it'sOK . if a new install, then RCD must be added, preferably to all circuits in bathroom. if client refuses, walk away.
 
As soon as it involves adding cable between lights, it’s an alteration, so minor works and rcd required.

Asking the question, as I’m sure we’ve all been in similar situations.... but maybe an enclosure on the outgoing circuit from the Fusebox containing an rcd?
 
Hi all,
I got job which client ask me to replace 20 down lights and install new bathroom extractor fan but DB is not RCD protected.(client dose not want change DB )
can I do my job without changing DB or I must change DB?
Thank you
You will be expected to provide RCD protection for the Bathroom.
 
Do the lights replacements and while you are there cost em up a new rcbo consumer unit and try to sell them on the added benefits of an upgraded fuse board.
if they don’t want the consumer unit you can’t force them and just bill em for the lights
 

Reply to No RCD Protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
429
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
546
Question is does this DB really need RCD protection as there are only internal lights and sockets supplying this large building that used to be a...
Replies
13
Views
562
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
772
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock