Discuss No thanks in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
645
Called out to a house where rcd is tripping,been going off over a period of weeks.
Did insulation test,got pretty good readings overall,except one circuit,which gave me a L/E,N/E reading of 0.40 meg ohms.
This was a sub main to a garage,found lighting to be at fault,disconnected.
Re did test ,all ok.
The rcd is upfront supplying 8way DB,later got a call back to say still tripping,so it can't be the lights in the garage.
Tried to explain the difficulties of finding exactly what it might be,but she's only interested in getting her lights in the garage back on ,it's gonna be one of those weeks I think.
Wondering if any of you,have had the same moarning,it's all your fault customers.
 
No all my Customers are heaven sent!!!:rolleyes:
 
Called out to a house where rcd is tripping,been going off over a period of weeks.
Did insulation test,got pretty good readings overall,except one circuit,which gave me a L/E,N/E reading of 0.40 meg ohms.
This was a sub main to a garage,found lighting to be at fault,disconnected.
Re did test ,all ok.
The rcd is upfront supplying 8way DB,later got a call back to say still tripping,so it can't be the lights in the garage.
Tried to explain the difficulties of finding exactly what it might be,but she's only interested in getting her lights in the garage back on ,it's gonna be one of those weeks I think.
Wondering if any of you,have had the same moarning,it's all your fault customers.

Did you test the RCD to see if it's tripping at the correct differential current?
Worth clamping the tails and checking what the actual leakage is when the installation is in use.
 
Did you test the RCD to see if it's tripping at the correct differential current?
Worth clamping the tails and checking what the actual leakage is when the installation is in use.
Yea did all the usual tests,& at 1/2 rated current it tripped,then tested all again & it didn't trip,but I did say to the customer it may need replacing.
A look of shock & amazement, & trying to do the best for her,said hopefully disconnecting the garage lights may have solved it.
My luck ran out ha ha .
 
At nearly half a Meg Im surprised it tripped my money is on something plugged in as well or with a up front RCD build up normal leakage (I know the word starts with a C but can I think of it no)

230/0.03
 

Reply to No thanks in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
895
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
815
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
646
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock